Welcome to Reef Forum R2R
+ Reply to Thread
Page 1 of 2 12 LastLast
Results 1 to 20 of 23
  1. #1
    Registered Member lemonyx is on a distinguished road
    Join Date
    May 2009
    Location
    Portland,OR
    Posts
    82

    ATO Cycling too much

    My relay clicks on and off every couple of minutes and want to change that. Any Ideas??

    Sorry no pixs, PC not reading the flash card

    Anyway I have a float switch located in the return area of the sump
    (before water)
    The switch connects to a relay and is on low voltage, 12v DC, the relay kicks on and activates a Power Head and a solenoid (to stop siphoning) that pumps RO/Di from a 55gal barrel thru a DIY kalk reactor and back to the sump. There's a way to wire it up to leep just this from happening, but at the moment I have a big brain FART

  2. #2
    Fish Pro
    jaytizzle is on a distinguished road
    Join Date
    Aug 2009
    Location
    Baton Rouge, LA
    Posts
    736
    Not sure why you're worried about many short cycles. I use a Tunze Osmolator connected to a reservoir (that automatically re-fills itself based on float switch sequences) and it cycles several times throughout the day. A very small change in water level in my sump causes the pump to turn on, run for a short time, then turn back off. This system in particular is designed for very precise level control.

    Regardless, I'm not sure how much I can help you. I run all of my control through an Apex and I could advise programming there but not sure how to work your situation.

  3. #3
    Registered Member OhYeah is on a distinguished road
    Join Date
    Nov 2010
    Location
    Florida
    Posts
    47
    If you have an apex, you can set a delay so it won't turn on and off with the slightest water movement.

  4. #4
    Registered Member OhYeah is on a distinguished road
    Join Date
    Nov 2010
    Location
    Florida
    Posts
    47
    Some people also put slash guard around the float switch (float switch inside a medicine bottle with holes)

  5. #5
    Registered Member lemonyx is on a distinguished road
    Join Date
    May 2009
    Location
    Portland,OR
    Posts
    82
    Thank's guys, took care of it for now, just added a piece of round acrylic to encase the switch with vents at the top. When i get my Apex, I'll hit you guy's up for programming help.

    thanks again

  6. #6
    Registered Member ModAquatics is on a distinguished road
    Join Date
    Nov 2011
    Location
    Katy, Texas
    Posts
    19

  7. #7
    Registered Member scrapz is on a distinguished road
    Join Date
    Dec 2008
    Posts
    360
    Your return chamber is too small. I have the same problem which is why I plan to make the return chamber at least 12"+ in my next sump

  8. #8
    Registered Member beaslbob is on a distinguished road
    Join Date
    May 2009
    Location
    huntsville, al
    Posts
    1,152
    you could use a lower relay to turn it on and an upper relay to turn it off.

    but I havent designed any ato's so have no experience.

  9. #9
    Registered Member ModAquatics is on a distinguished road
    Join Date
    Nov 2011
    Location
    Katy, Texas
    Posts
    19
    Quote Originally Posted by beaslbob View Post
    you could use a lower relay to turn it on and an upper relay to turn it off.

    but I havent designed any ato's so have no experience.
    Yes, That can be done but the problem is that you should always have 2 float switches for each circuit for redundancy since float switches will fail eventually. So if you did upper and lower limit switches you would need 4 float switches. Also, the 2 submerged switches would constantly be submerged which would increase the chance of algae or snails, etc. messing it up. However, if you still want to do it that way then here is how; (courtesy of Chicago Sensor)
    Physics are unbreakable laws discovered by man that were made by creation.....

  10. #10
    Registered Member lemonyx is on a distinguished road
    Join Date
    May 2009
    Location
    Portland,OR
    Posts
    82
    Thanks for the help, that clears it up

  11. #11
    Registered Member blurry is on a distinguished road
    Join Date
    Dec 2009
    Location
    liverpool, ny (north of Syracuse, NY)
    Posts
    208
    having two switches wired together with the backup above the other for redundency is very preferred (if one sticks in the full position the other will act as the float switch)

    Easiest way to ATO is with a controller: set to have a set timer run for X seconds when activated. I run a maxijet1200 for 30 seconds when the ATO is tripped, and force it off for 9:30 seconds after. This has a few benefits - (1) the RODI is connected to my topoff, so it isn't constantly being hammered on (2) even if all goes wrong I only add 30 seconds of water every 10 minutes so the flooding is reduced.

  12. #12
    Registered Member
    AZDesertRat is on a distinguished road
    Join Date
    Feb 2009
    Location
    Phoenix AZ
    Posts
    1,698
    Two or three float switches is much better than one since it gives you both a range between on and off plus a redundant emergency off. One switch is like having a float valve with very limited range.

  13. #13
    Registered Member blurry is on a distinguished road
    Join Date
    Dec 2009
    Location
    liverpool, ny (north of Syracuse, NY)
    Posts
    208
    The emergency off is a good addition. Using it as a high stop adds more switches that can fail. Timer is preferred IMO

  14. #14
    Registered Member
    AZDesertRat is on a distinguished road
    Join Date
    Feb 2009
    Location
    Phoenix AZ
    Posts
    1,698
    Good switches rarely fail.
    I use the Ultra Precise Level Controller-II found on sale here:
    Untitled Document

    for my ATO in the sump and the Solenoid Valve Controller in my 23 gallon ATO reservoir like found here:
    Solenoid Valve Controller by SpectraPure

    The UPLC gives me between 1/10" and 4" user adjusted range, can be adjusted to 10 different fill rates and uses the same peristalticpump as their popular LiterMeter so is bulletproof.

    The Solenoid kit uses the very robust horizontal type float switches that are completely encapsulated so rarely fail.

  15. #15
    Registered Member jelly is on a distinguished road
    Join Date
    May 2011
    Location
    Wisconsin
    Posts
    382
    when you set your ATO up with 2 switches should the switches be on the same BB outlet number or on 2 different BB outlets for the apex

  16. #16
    Registered Member blurry is on a distinguished road
    Join Date
    Dec 2009
    Location
    liverpool, ny (north of Syracuse, NY)
    Posts
    208
    I like those switches, look like pressure based like avast is using.

  17. #17
    Fish Pro
    jaytizzle is on a distinguished road
    Join Date
    Aug 2009
    Location
    Baton Rouge, LA
    Posts
    736
    Quote Originally Posted by jelly View Post
    when you set your ATO up with 2 switches should the switches be on the same BB outlet number or on 2 different BB outlets for the apex
    you want them as 2 different switches. I have mine with a low level switch to turn on my RODI unit, a high level switch to turn it off, and an emergency high level switch to serve as a backup in case the first one fails and also sends me a notification that it got too high and the first float failed. Mine are in RODI storage, though, so it's not likely they'll fail as there's nothing to build up on them.

  18. #18
    Registered Member Hahnmeister is on a distinguished road
    Join Date
    Oct 2009
    Location
    Milwaukee
    Posts
    160
    There is a simple non-electronic way to solve this:

    Take the ouptut hose from the ATO that supplies fresh water to the sump and raise it up a little, then wrap it like a coil around something so that it is still a downward slope at all times (think giant waterslide). You may need to add some hose as well.

    This way, the ATO will turn on, but no water will actually enter the sump for a bit... it will be taking its time going down the loop. When water starts to enter the sump, the hose will be filled with water still, so even after the ATO shuts off, it will continue to drain more water into the sump. This way, you will have less frequent top-off cycles that each add more water.

    Another method is to have the ATO water enter a cup or other container with a small hole in the bottom. If you make the hole small enough to restrict the ATO's output to a lower flow rate, it will take longer to fill, right? And in the meantime the ATO will fill up the cup so that after the ATO shuts off, water will continue to flow into the sump. Just make sure that the duration that the ATO is on will not cause the cup to overflow, as in: make your cup big enough or give it a backup overflow port (I just position my cup in the sump so if it overflows, its into the sump).

    Otherwise, yes, I think having a small arduino or other microcontroller based ATO is smart so you can program in other failsafes like "delay before turn on" to eliminate wave triggers, "maximum duty cycle" to prevent overflows from float failure or a leak, "minimum duty cycle" to prevent ATO cycles that are too small, and with a microcontroller, you can even make it so that it logs the info or reports its on/off times to the web or sends you an emergency email or text should the ATO sense an emergency. To solve this problem however, all you need is a cup or some extra hose.
    Last edited by Hahnmeister; 12-20-2011 at 05:58 PM.

  19. #19
    Registered Member
    AZDesertRat is on a distinguished road
    Join Date
    Feb 2009
    Location
    Phoenix AZ
    Posts
    1,698
    Those suggestions may work for a Pico system but for anything of size its not going to solve anything.

  20. #20
    M@!
    M@! is offline
    Registered Member M@! is on a distinguished road
    Join Date
    Oct 2011
    Location
    Dallas, TX
    Posts
    336
    You could always put it on an appliance timer that runs for 15 minutes every two hours.

 

 

Similar Threads

  1. Cycling Help
    By Californiareef in forum Reef Aquarium Discussion
    Replies: 5
    Last Post: 09-05-2011, 03:51 PM
  2. Cycling?
    By MurseBS in forum Reef Aquarium Discussion
    Replies: 14
    Last Post: 08-01-2011, 06:58 PM
  3. Replace LR Without Cycling?
    By Bongo Shrimp in forum Reef Aquarium Discussion
    Replies: 8
    Last Post: 06-20-2010, 09:06 PM
  4. Cycling
    By Striike in forum Chattanooga Reef Club
    Replies: 30
    Last Post: 12-08-2009, 08:10 PM
  5. Cycling ??
    By lemonyx in forum New To The Hobby? (SW Beginner Forum)
    Replies: 8
    Last Post: 07-06-2009, 05:40 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts