How to wire a GFCI outlet

skinz78

10K Club member
View Badges
Joined
May 8, 2009
Messages
21,934
Reaction score
648
Location
lovely rainy NW Washington
Rating - 0%
0   0   0
Disclaimer.
I am a licensed electrician, my way of doing electrical work is just my interpretation of the National Electrical Code and what I feel is good workmanship. Every electrician has their own interpretation of the code and in some cases do electrical work in other ways than I do. I am not saying my way is the only way, but it is how I have done it for eleven years now.
The most important thing to remember when doing electrical work is to make very good connections. Loose wires cause fires. This is no joke just a plain fact, that should be written in the Bible. :angel:The second most important thing to do is make sure all power is turned off before working on anything. Getting shocked sucks, believe me.

OK now that I am done with my rant I will do a step by step explanation on how to wire a GFCI with outlets protected by it down stream. : FIRST THINGS FIRST, disconnect all power.

The visual difference between a GFCI and a standard outlet, the GFCI is on the left.
IMG_2890.jpg


Now you can wire one GFCI up so it protects all other outlets downstream of it. Or you can just buy a GFCI for every outlet you want protected. It is cheaper to buy one GFCI and then protect each outlet downstream but it is a little more complicated to do it that way. I am not a prices guy but I think the GFCI's are about $10 ea compared to a buck or two for normal outlets. I am going to show you how to do it with one GFCI protecting other outlets in this thread.
GFCI's have two spots to put sets of wires in them, they are labeled LINE and LOAD. In this pic you will see LINE on the right side and LOAD on the left side.
IMG_2893.jpg


GFCI's need the power coming in to them to be on the LINE side of the outlet and whatever it is to protect downstream of the GFCI hooks to the LOAD side. Just remember the LOAD is what the GFCI is driving. Sorry my pic on the right the wording is cut off. It says power from panel.
IMG_2899.jpg


Now I have ran the wire in between the two boxes and in this picture you can see the wire coming into the box. But more importantly you can see the yellow outer shield "sheathing" of the wire. This pic is to demonstrate the proper amount of sheathing to be in the box. On the left you can see I have about 3/8" of sheathing in the box and on the right you can see I have about 1 1/4" of sheathing in there. This is a minimum and maximum amount. Also for stapling you don't want to staple too hard, just enough to hold the wire in place without cutting into the sheathing.
IMG_2918.jpg


Now you will have black, white, and a bare or green ground wire. Now assuming your house is wired correctly, the black wire is almost always your power or positive wire. The white wire is almost always your neutral or negative wire, and the bare or green is your ground. On most GFCI brands you can usually put 2 power and 2 neutral LINE wires to the outlet. There should also be spots to put 2 power and 2 neutral LOAD wires to the outlet. But there is only one spot to attach the ground wire to the GFCI so you will need to wire nut them all together with a single "pigtail" to attach to the GFCI. I take and push all the ground wires down into the bottom corner of the box so they are all grouped together.
IMG_2903.jpg


Then trim them all the same length about 2" out of the box. Next take a scrap of ground wire "approx 12 inches or longer" and wire nut it in with the wires coming out of the box. Once this is done neatly fold the wire nut and the wires back into the box.
IMG_2906.jpg


Next I take the set "black and white" that I know is my LINE "power coming from the panel" and gently twist them up to mark them as different than the others.
IMG_2907.jpg


At this point you are ready to fold and cut all the wires to final length. I fold them all to the bottom and to the back as neatly as possible. Then I place my hand on them to measure, all you need is one hand length coming out of the box.
IMG_2909.jpg


Next strip all the wires about 3/4" long, but I leave some of the wrap on the LINE wire.
IMG_2911.jpg


You are now ready to connect the wires to the GFCI. Remember it is important to keep your LINE and LOAD separate and hook them where they are labeled to go. One other way to know where where the power and neutral wire go's is that the silver screw is the neutral and the gold is the power. Notice no visible copper wire is showing, this is what you want. Exposed can short out.
IMG_2914.jpg


Finally you can neatly as possible fold the wire back into the box thus pushing the GFCI into the box as well. make sure your bare ground wire isn't touching any of the white or black screws or bare copper.
IMG_2915.jpg


OK now screw in the GFCI and put the plate on and installation is complete.

Next I am going to show you how to install a 2 gang or quad outlet. Basically it is 4 spots to plug into in one box. You will need a 2 gang box for this. In my application I have a wire in and a wire out to the next outlet. Now remember these are all on the LOAD side of the GFCI and are protected.
One major difference in this application is you will need two ground wires, one for each outlet. In this pic I have the two ground pigtails and I have take one set of black and white wires and trimmed them to hand length. The second set of black and white wires I leave long.
IMG_2919.jpg


The long wires I strip at hand length and wrap it around the outlet screw. This leaves a long pigtail coming off of the screw. This pigtail later connects to the second outlet. Sort of a jumper. Notice I have my wires wrapped tightly to the screws and going clockwise so when I tighten the screw it pulls the wire under it instead of pushing it out.
IMG_2922.jpg


Once all connections are made to the first outlet you can screw it into the box. Then you will have the single ground, one long black and one long white wire left over. Push them into the back and bottom of the box and cut them hand length.
IMG_2925.jpg


Then connect the second outlet up and screw it into the box, add your cover plate then you should be done.
IMG_2927.jpg


Turn your breaker back on and reset the GFCI, you should then have power to all your outlets.:smile:

If you have any questions please feel free to ask!

Ok one last final rant :sad:
You need GFCI outlets, plain and simple with no exceptions. There is a lot of debate on this. Some people say well what if you aren't home and the GFCI trips. My response to that is what if you are working on your tank with your arm in the water while standing in a puddle and the water comes in contact with the electrical outlet. Simple, the GFCI trips. Now imagine the same scenario but with no GFCI protection and lets throw in a heart condition that you didn't know about. What happens is you get shocked, the electricity takes the quickest path to ground which just happens to be through your body to the wet puddle you are standing in. The electricity flows through your body and in doing so passes through your heart causing it to cease to beat. Now what is a bigger problem, your heart beat stopping or you take doing a full on nuke caused by a tripped GFCI while you were away? I do realize I just threw a lot of what if's out there but I truly feel I don't want the chance of a what if to happen to me, do you?
 
Last edited by a moderator:

Wy Renegade

Zs and Ps/PE collector
View Badges
Joined
Feb 5, 2009
Messages
3,785
Reaction score
156
Location
Wyoming
Rating - 0%
0   0   0
Nice thread Chris and great post on the wiring! Another alternative for those who aren't as handy as others is to consider a power strip with a true GFCI breaker built in. Not a surge protector like you would buy for a computer, but a true GFCI that works just like the outlet above.

I believe these Belkin ones are now discontinued, but there are other brands of these available;

MiscBelkinPowerstrip25March09.jpg


Please be aware that the coralife timer strips DO NOT have a GFCI built in to them, and this is what happens when they make contact with saltwater;

MiscMeltedCoralifePowerstrip28Feb08.jpg


In this particular case, a GFCI may have saved $100.00s of dollars in tank equipment, including several powerheads as well as the light and labor to replace a fried breaker. Fortunately, nobody was hurt.

Having a GFCI not only protects your life and your livestock, it also protects your equipment.
 
OP
OP
skinz78

skinz78

10K Club member
View Badges
Joined
May 8, 2009
Messages
21,934
Reaction score
648
Location
lovely rainy NW Washington
Rating - 0%
0   0   0
Good point, I have also used one of the GFCI powerstrips on my old tank because I couldn't get to the outlet after the tank was set to replace it with a GFCI.

That is scary on the Coralife timer, I use one for my lighting... But it is GFCI protected and is on the top of my aquarium hood well away from the water.
 

Wy Renegade

Zs and Ps/PE collector
View Badges
Joined
Feb 5, 2009
Messages
3,785
Reaction score
156
Location
Wyoming
Rating - 0%
0   0   0
I have the same problem on my 65gal, thats why I hunted that belkin down a few years ago.

On the timer, this particular one was supposed to be up on a ledge, well away from the water. But, somebody had knocked it down and they overfilled the tank slightly. The overspill happened to land on the timer strip - snap, crackle, fizzle, and the lights went out and the power along the entire back side of the building shut down. Fortunately the tank/timer was sitting on a countertop so nobody was standing in the puddle of water.
 

mdb_talon

2500 Club Member
View Badges
Joined
Dec 6, 2010
Messages
4,938
Reaction score
7,756
Location
Illinois
Rating - 0%
0   0   0
I previously used powerstrips with built in GFCI on a tank and every single time the power would go out for even a second it would trip the GFCI when power came back on. I tried two seperate strips (different types/brands) and it was the same problem. Finally after a day the tank went without power (due to a blip where we only probably lost power a few seconds) I wired a GFCI receptacle to the fish tank in question. Never had issues like that since. I dont have any idea if my experience with the strips was unlucky or uncommon, but just wanted to throw it out there.
 

Wy Renegade

Zs and Ps/PE collector
View Badges
Joined
Feb 5, 2009
Messages
3,785
Reaction score
156
Location
Wyoming
Rating - 0%
0   0   0
mdb I've never had any issues with my belkin kicking back on without throwing the GFCI due to power outages, but I can't speak to any of the other brands.
 

fsu1dolfan

2500 Club Member
View Badges
Joined
May 9, 2008
Messages
2,642
Reaction score
53
Location
South Florida
Rating - 0%
0   0   0
Skinz - Great writeup and pics...i have been meaning to switch my current outlets to GFCI. Maybe ill get some motivation to do it soon.
 

Reef Breeders

ReefBreeders.com
View Badges
Joined
Dec 21, 2010
Messages
4,521
Reaction score
758
Location
North Kingstown, RI
Rating - 0%
0   0   0
I hate gfcis, they are verrrrry picky. You cant just piggy back a wire on the load side, you NEED a line and load. IE, if the outlet goes out, anything on the line end also goes out. It will not turn on unless it is wired that way.
 

greg0385

Valuable Member
View Badges
Joined
Jan 23, 2011
Messages
1,355
Reaction score
25
Location
summertown,tn
Rating - 0%
0   0   0
great thread, brings back memories of electrical schooling (i took that i never used). if im not mistaken(which i may be) all houses now have to have these and i want to say they want to have AFCI's(Arc Fault something something) too....... might have to break out my NEC code book to read up on that again.
 

nixer

Valuable Member
View Badges
Joined
Apr 27, 2010
Messages
1,321
Reaction score
4
Location
indiana
Rating - 0%
0   0   0
Only near water, like in kitchens and baths

not always. there are some state, county, and town codes that require them in garages or anything subgrade. im sure there has to be somewhere that requires them in the entire house.
 
OP
OP
skinz78

skinz78

10K Club member
View Badges
Joined
May 8, 2009
Messages
21,934
Reaction score
648
Location
lovely rainy NW Washington
Rating - 0%
0   0   0
The NEC requires any outlets within 6' of a sink, all kitchen outlets, all bath outlets, all outside outlets, all garage outlets including the door opener, and all crawlspace outlets.
 

mikezalewski

Community Member
View Badges
Joined
May 11, 2011
Messages
67
Reaction score
0
Location
michigan
Rating - 0%
0   0   0
This is a good DIY posting because this is where the complete system starts from and ends with if not careful. The one thing to make this better is the idea that you can also talk to the electrical employees in Home Depot or Lowes and ask them how to wire this up they can usually help as well!
 

iprayforwaves

Community Member
View Badges
Joined
Jul 18, 2011
Messages
66
Reaction score
35
Location
Orlando, FL
Rating - 0%
0   0   0
Run all my tanks with GFI Outlets, thought I'm not electrically capable enough to wire them up myself. Very informative post!
 

Acipenser

New Member
View Badges
Joined
Feb 17, 2012
Messages
14
Reaction score
1
Location
Georgia
Rating - 0%
0   0   0
I am not an electrician - so please check with one before doing any of this yourself.
You can also wire multiple GFCI outlets so that they will only trip the individual set of outlets where the fault occurred.

Personally I prefer this method, as one faulty piece of equipment does not shut down the whole series of outlets. It is more expensive, but it allows me to isolate the individual fault and keep the rest of the outlets running. This can only be done with multiple GFCI outlets. Normal outlets will not offer any protection down the line.

This can be done by daisy chaining the outlets off the line side of the outlet. Power goes into the line side of one outlet, and out the line side of the same outlet to the line side of the next outlet. Very similar to the original post, just don't use the load side.
 

Mike&Terry

Wrasses, Angels, & Tangs, Oh My!
View Badges
Joined
Oct 7, 2011
Messages
6,124
Reaction score
1,834
Location
Chesterfield, VA
Rating - 0%
0   0   0
Great thread Chris!
There are so many excellent tips in here for the DIY'er. I always prefer to use the screws for making connections to outlets versus using backstab connections. Depending on the quality of the outlets, and the gauge wire being used, those backstab connections can cause problems, IME.
 

redtop03

Well-Known Member
View Badges
Joined
Oct 12, 2009
Messages
965
Reaction score
17
Location
Barbourville
Rating - 0%
0   0   0
Great thread Chris!
There are so many excellent tips in here for the DIY'er. I always prefer to use the screws for making connections to outlets versus using backstab connections. Depending on the quality of the outlets, and the gauge wire being used, those backstab connections can cause problems, IME.

+1...the push in connection on the back only has a tiny flat piece that bites into the wire and is very prone to loosing connection after the copper wire has aged/tarnished,using the screws is a much better idea
 
OP
OP
skinz78

skinz78

10K Club member
View Badges
Joined
May 8, 2009
Messages
21,934
Reaction score
648
Location
lovely rainy NW Washington
Rating - 0%
0   0   0
Great thread Chris!
There are so many excellent tips in here for the DIY'er. I always prefer to use the screws for making connections to outlets versus using backstab connections. Depending on the quality of the outlets, and the gauge wire being used, those backstab connections can cause problems, IME.

I am an electrician and you wouldn't believe how many service calls I get because people use the stab in type outlets... Money in my pockets LOL!
 

Reef Breeders

ReefBreeders.com
View Badges
Joined
Dec 21, 2010
Messages
4,521
Reaction score
758
Location
North Kingstown, RI
Rating - 0%
0   0   0
LOL those things always fail, I am phasing them out of my house gradually, whenever I run a new line for a light, outlet, etc. I re do the outlet, the wires rip out just by working in the box.
 