I thought I would freshly post this in the New Reef Tank Beginners Section.
I'm about to fix things after experiencing dangerous situation with my Tank Setup. (but wanted to share this while it's fresh in my head)
I'm an Electrical/Electronic Computer System Engineer and I know a bit about Electrician Stuff too (but little about how GFCI outlets work)
I had some luck today as I prepared to put both my arms into my Tank to clean up and add corals.
During Prep I spilled some water as I was preparing and my rubber Crocks got a bit wet, so it connected my feet electrically to my Basement Floor (which is a raised subfloor, but enough water spilled to also drip onto the Concrete Floor (GROUND).
I was scooping some more water using a jug when I felt a tingle at my finger tips.
Then I touch the tip of my finger to tank water and felt a much stronger electrical pulse.
So I got my AC volt meter and with one end on Ground (Concrete Floor), I touched THE (+) lead of my volt meter to water and I got 96 Volts reading.
THE TANK was High Voltage and Dangerous!!! Could kill !!!
I got insulated goves. Put on my best insulated shoes, and had son at the Main House breaker while I tested things.
With the Voltmeter on tank, I started one by one pulling plugs (I have many)….
Almost no plugs left in outlets, and after moving things around, ( the VOLTGE rose to 110Volts).
Finally two plugs left, I removed the Next one and VOLTAGE went away. I found the Fault.
It was my sea swirl water oscillator. It was wet and dripping from inside. Inside I know is a small AC motor and there are O-Ring in connectors, so they wore out. Probably a drip inside.
That was puzzling since I have a GFCI outlet and a ground probe. So I looked from my Ground Probe which was in Sump.
But it was missing. It fell out and was behind sump. Possibly jarred loose during maintenance.
I put back the Ground Probe, and plugged in the Faulty Sea Swirl (RIGHT AWAY the GFCI protection SHUT EVERYTHING OFF).
I've learned a similar Lesson before, so my tanks have always been protected by GFCI (Ground Fault Circuit Intertupt OUTLETS).
What I learned a few years ago, is GFCI doesn't always work, if there is no Ground Probe to Ground the Tank water.
Over the years, pumps, heaters have cracked and caused High Voltage in my systems, and most of the time GFCI would trip and turn off AC power (with GFCI and Ground Probe).
What I ALSO learned a few years ago is an Urchin chewed thru a wire insulation and stripped the AC Wire to copper. That electrified my tank but since the Heater Like most heater don't have a ground pin plug (ie 3 Prong), the tank was 110Volts. I had no ground probe, and GFCI didn't trip since HEater had no ground to trigger GFCI.
GFCI outlet don't work if TANK isn't grounded, and HOT wire voltage electrifies the Tank.
If your (hands to feet) become the ground CONNECTOR, it may trip the GFCI. BUT will it work, will if be fast enough, that is something I don't plan on testing.
So I'm about to BOLT/Tie-Wrap that ground PROBE back into my setup. All my ground probes since I have one is each sump and one in each tank (except one, which I will also now add).
Hope you all have a Safe Reefing Experience for many years.
If you have "NO GROUND PROBE" on your setup you run a risk of a ZAP or electrocution.
I you have "NO GFCI on your SETUP" You may DIE SOME DAY (or maybe someone you care about)
----------------- NOV 26 ---- UPDATE --- 3 DAYS LATER -----------------
Did a video Testing how GFCI vs GFCI with Ground Probes (Works and Does Not work)
** When a Heater Fails, AC Pump Fails, or Urchin Chews up your AC Power Cord **
** THIS IS ALSO not just your Tank/SUMP...Applies to where you mix up water, and heat it and can have spills **
More discussion below about GFCI, and Probes.
I'm about to fix things after experiencing dangerous situation with my Tank Setup. (but wanted to share this while it's fresh in my head)
I'm an Electrical/Electronic Computer System Engineer and I know a bit about Electrician Stuff too (but little about how GFCI outlets work)
I had some luck today as I prepared to put both my arms into my Tank to clean up and add corals.
During Prep I spilled some water as I was preparing and my rubber Crocks got a bit wet, so it connected my feet electrically to my Basement Floor (which is a raised subfloor, but enough water spilled to also drip onto the Concrete Floor (GROUND).
I was scooping some more water using a jug when I felt a tingle at my finger tips.
Then I touch the tip of my finger to tank water and felt a much stronger electrical pulse.
So I got my AC volt meter and with one end on Ground (Concrete Floor), I touched THE (+) lead of my volt meter to water and I got 96 Volts reading.
THE TANK was High Voltage and Dangerous!!! Could kill !!!
I got insulated goves. Put on my best insulated shoes, and had son at the Main House breaker while I tested things.
With the Voltmeter on tank, I started one by one pulling plugs (I have many)….
Almost no plugs left in outlets, and after moving things around, ( the VOLTGE rose to 110Volts).
Finally two plugs left, I removed the Next one and VOLTAGE went away. I found the Fault.
It was my sea swirl water oscillator. It was wet and dripping from inside. Inside I know is a small AC motor and there are O-Ring in connectors, so they wore out. Probably a drip inside.
That was puzzling since I have a GFCI outlet and a ground probe. So I looked from my Ground Probe which was in Sump.
But it was missing. It fell out and was behind sump. Possibly jarred loose during maintenance.
I put back the Ground Probe, and plugged in the Faulty Sea Swirl (RIGHT AWAY the GFCI protection SHUT EVERYTHING OFF).
I've learned a similar Lesson before, so my tanks have always been protected by GFCI (Ground Fault Circuit Intertupt OUTLETS).
What I learned a few years ago, is GFCI doesn't always work, if there is no Ground Probe to Ground the Tank water.
Over the years, pumps, heaters have cracked and caused High Voltage in my systems, and most of the time GFCI would trip and turn off AC power (with GFCI and Ground Probe).
What I ALSO learned a few years ago is an Urchin chewed thru a wire insulation and stripped the AC Wire to copper. That electrified my tank but since the Heater Like most heater don't have a ground pin plug (ie 3 Prong), the tank was 110Volts. I had no ground probe, and GFCI didn't trip since HEater had no ground to trigger GFCI.
GFCI outlet don't work if TANK isn't grounded, and HOT wire voltage electrifies the Tank.
If your (hands to feet) become the ground CONNECTOR, it may trip the GFCI. BUT will it work, will if be fast enough, that is something I don't plan on testing.
So I'm about to BOLT/Tie-Wrap that ground PROBE back into my setup. All my ground probes since I have one is each sump and one in each tank (except one, which I will also now add).
Hope you all have a Safe Reefing Experience for many years.
If you have "NO GROUND PROBE" on your setup you run a risk of a ZAP or electrocution.
I you have "NO GFCI on your SETUP" You may DIE SOME DAY (or maybe someone you care about)
----------------- NOV 26 ---- UPDATE --- 3 DAYS LATER -----------------
Did a video Testing how GFCI vs GFCI with Ground Probes (Works and Does Not work)
** When a Heater Fails, AC Pump Fails, or Urchin Chews up your AC Power Cord **
** THIS IS ALSO not just your Tank/SUMP...Applies to where you mix up water, and heat it and can have spills **
More discussion below about GFCI, and Probes.