I have been searching, and think I figured this out, but I"m nervous so I'm asking. This is for an APEX Classic.
I have floats:
1) ATO_L that says "not enough water"
2) ATO_H that says "Stop, I'm drowning"
I also created a Virtual outlet ATO_MAX
What I want to happen:
1) If water is low for at least 1 minute, turn on
2) if water is too high, don't turn on
3) If on, don't stay on for more than 5 minutes
4) Once off, don't turn on for 360 minutes
My code:
ATO Outlet:
Fallback OFF
Set OFF
If ATO_L CLOSED Then ON //not enough water
If ATO_H OPEN Then OFF // I'm drowning
If Output ATO_MAX = ON Then OFF //Its been 5 minutes, shutoff
Defer 001:00 then ON //don't turn on unless low for a minute
Min Time 360:00 Then OFF // Once off, stay off for 3 hours
My ATO_MAX Virtual outlet:
If Output ATO = ON Then ON //If on then on
Defer 005:00 Then ON // but wait 5 minutes before turning on
I have floats:
1) ATO_L that says "not enough water"
2) ATO_H that says "Stop, I'm drowning"
I also created a Virtual outlet ATO_MAX
What I want to happen:
1) If water is low for at least 1 minute, turn on
2) if water is too high, don't turn on
3) If on, don't stay on for more than 5 minutes
4) Once off, don't turn on for 360 minutes
My code:
ATO Outlet:
Fallback OFF
Set OFF
If ATO_L CLOSED Then ON //not enough water
If ATO_H OPEN Then OFF // I'm drowning
If Output ATO_MAX = ON Then OFF //Its been 5 minutes, shutoff
Defer 001:00 then ON //don't turn on unless low for a minute
Min Time 360:00 Then OFF // Once off, stay off for 3 hours
My ATO_MAX Virtual outlet:
If Output ATO = ON Then ON //If on then on
Defer 005:00 Then ON // but wait 5 minutes before turning on