I've setup an FMM with a lo and hi sensor in my 65 gallon fresh water barrel. My hope is that if the barrel gets to ~30 gallons (where the bottom sensor is) it will open the solenoid and run my RODI until the hi sensor is closed. Right now, the lo sensor is acting like ATO and turning on/off only based on the open/close of the lo sensor. My code is below; please help!


Fallback OFF
Set OFF
If AWClow OPEN Then ON
If AWCHi CLOSED Then OFF
When On > 360:00 Then OFF
 

SuncrestReef

That Apex guy
View Badges
Joined
Jan 18, 2018
Messages
4,214
Reaction score
9,214
Location
Oregon
Rating - 0%
0   0   0
Just remove the Set OFF command. That command becomes the only True condition when the water is above the low sensor but has not yet reached the upper sensor, so it shuts off the solenoid prematurely.

Fallback OFF
If AWClow OPEN Then ON
If AWCHi CLOSED Then OFF
When On > 360:00 Then OFF
 