I guess I was just curious as to how it was tripping a circuit it wasn't on. Must be leaking voltage into the water and getting picked up somewhere thus tripping the circuit... one thing after another...
Let me tell you my story I had a heater doing the same thing and in the process of diagnosis just like you I kept putting it in the water and watching the GFI Outlet keep popping until the one time I put it in there and it literally blew the heater apart shattering the tank. Be careful
 
OP
OP
Pico bam

Pico bam

Well-Known Member
View Badges
Joined
Jul 28, 2019
Messages
977
Reaction score
1,630
Location
Lake elmo
Rating - 0%
0   0   0
No offense but are you sure you're not sharing a neutral wire between the circuits?
This question goes over my head a bit unfortunately. Im Experimenting with a multimeter instead of my finger now. I can say my brother (an electrician) did the heavy lifting on this one.
Let me tell you my story I had a heater doing the same thing and in the process of diagnosis just like you I kept putting it in the water and watching the GFI Outlet keep popping until the one time I put it in there and it literally blew the heater apart shattering the tank. Be careful
Thank god your a Ford tech and not a gm otherwise you might not be with us anymore.
 
OP
OP
Pico bam

Pico bam

Well-Known Member
View Badges
Joined
Jul 28, 2019
Messages
977
Reaction score
1,630
Location
Lake elmo
Rating - 0%
0   0   0
After much contemplation and experimenting with a multimeter. Its the skimmer pump when plugged in and a multimeter connected to a ground and point of sale in the water there 120ish volt reading. When unplugged there nearly nothing. So the heater was acting as a ground so to speak and tripping the gfci. As far as I can tell.

With the skimmer pump unplugged I was able to plug the heater back in.
 

emain879

Active Member
View Badges
Joined
Oct 25, 2020
Messages
132
Reaction score
46
Location
ellwood city
Rating - 0%
0   0   0
So during a power outage. I was running my heater and return pump on off a generator. When I go to plug everything back in this morning it was running fine. Came back a hour later power was off in the aquarium room. Thought it was a breaker in the box but turned out to be the gfci. I tried it three times whenever I plug in the inkbird it trips the gfci. Heres where it I get confused. I tried running it off a different circuit. Still trips the same gfci. Even though it on a different circuit. Is my heater to blame? Its a titanium 800w finnex. Im refreshing my basic understanding of a gfci right now. But thought I might get a quick answer on here.

Attached is a picture of why my power went out...

20220711_105813.jpg
It may be the heater, I had one do the same thing, then it exploded in my sump, had a heck of a mess
 
OP
OP
Pico bam

Pico bam

Well-Known Member
View Badges
Joined
Jul 28, 2019
Messages
977
Reaction score
1,630
Location
Lake elmo
Rating - 0%
0   0   0
and point of sale
I'm uncertain why it says point of sale here. I typed "point of sale in the water" its almost like this site automatically assuming point of sale is an acronym for point of sale and spelling it out.
 

KrisReef

10K Club member
View Badges
Joined
May 15, 2018
Messages
11,710
Reaction score
27,563
Location
ADX Florence
Rating - 0%
0   0   0
Man this is frustrating p.o.s. short for positive this really is something else
"Piece's of ships"_ is a known swear and these usages of terms get edited by the auto editor, routinely. My phone spell checker also autocorrects my typing and blows the CGFI on my pacemaker 4-5x's /day.
 

theMeat

2500 Club Member
View Badges
Joined
Oct 1, 2017
Messages
3,060
Reaction score
2,521
Rating - 0%
0   0   0
Yes I know I have 2 receptacles tied into the gfci, the gfci being in one of them. But I did try a different outlet on a different receptical on a different circut... and it tripped the gfci.

I'm attempting to use the correct terminology but I'm not proficient here...
The way a gfci works is it measures the loop, both sides, both hot and neutral. When a difference is detected between the 2 sides the gfci trips. You can rule out a problem with the hot side because that would trip the breaker. Couple of possibilities I can think of here.
- a ground is being used as a neutral somewhere on these circuits
- a neutral is being shared somewhere by these two circuits
- a ground and neutral are making contact on these circuits
- could be wet somewhere that’s chasing a contact between neutral and ground
- salt creep is making contact
 

theMeat

2500 Club Member
View Badges
Joined
Oct 1, 2017
Messages
3,060
Reaction score
2,521
Rating - 0%
0   0   0
After much contemplation and experimenting with a multimeter. Its the skimmer pump when plugged in and a multimeter connected to a ground and point of sale in the water there 120ish volt reading. When unplugged there nearly nothing. So the heater was acting as a ground so to speak and tripping the gfci. As far as I can tell.

With the skimmer pump unplugged I was able to plug the heater back in.
Wow, so two separate issues conspired against you.
Always a good idea to have a ground probe paired with a gfci
 

Dom

Full Time Reef Keeper
View Badges
Joined
Apr 29, 2016
Messages
5,803
Reaction score
6,362
Location
NY
Rating - 0%
0   0   0
I guess I was just curious as to how it was tripping a circuit it wasn't on. Must be leaking voltage into the water and getting picked up somewhere thus tripping the circuit... one thing after another...

Ok... did you test for stray current in the tank?
 
OP
OP
Pico bam

Pico bam

Well-Known Member
View Badges
Joined
Jul 28, 2019
Messages
977
Reaction score
1,630
Location
Lake elmo
Rating - 0%
0   0   0
Ok... did you test for stray current in the tank?
Yes when the old skimmer pump was plugged in there was 120ish stray volts. After that was unplugged there was 8 stray volts. After I plugged the heater back in it went down to hundredths of a volt. So the heater is acting as a grounding prob as someone mentioned earlier witch explains alot. Still don't like the 8 stray volts. If I have a little cut on my finger and put my hand in the tank I can feel a tingle like licking a 9v battery. So I'll be looking into where that lesser voltage is coming from now.
 

DanTheReefer

Active Member
View Badges
Joined
Dec 2, 2019
Messages
494
Reaction score
508
Rating - 0%
0   0   0
Yes when the old skimmer pump was plugged in there was 120ish stray volts. After that was unplugged there was 8 stray volts. After I plugged the heater back in it went down to hundredths of a volt. So the heater is acting as a grounding prob as someone mentioned earlier witch explains alot. Still don't like the 8 stray volts. If I have a little cut on my finger and put my hand in the tank I can feel a tingle like licking a 9v battery. So I'll be looking into where that lesser voltage is coming from now.
Yeah the little cuts burning is a thing, my Koralia did that, best to find the faulty equipment and throw it out before it gets worse. I don’t like grounding probes because they can mask issues. Although they could enable a GFCI to trip if there is a fault, rather than your body enabling the GFCI to trip. I still cringe a little bit when I put my hand in the tank after having two stray current issues
 
OP
OP
Pico bam

Pico bam

Well-Known Member
View Badges
Joined
Jul 28, 2019
Messages
977
Reaction score
1,630
Location
Lake elmo
Rating - 0%
0   0   0
Yeah the little cuts burning is a thing, my Koralia did that, best to find the faulty equipment and throw it out before it gets worse. I don’t like grounding probes because they can mask issues. Although they could enable a GFCI to trip if there is a fault, rather than your body enabling the GFCI to trip. I still cringe a little bit when I put my hand in the tank after having two stray current issues
I wish there was a decent way to test equipment for this. The best I've figured out is to use a multimeter positive end in the water and ground to an outlet ground. Then I go about plugging things in one by one.... gotta love used equipment.
 

theMeat

2500 Club Member
View Badges
Joined
Oct 1, 2017
Messages
3,060
Reaction score
2,521
Rating - 0%
0   0   0
Yeah the little cuts burning is a thing, my Koralia did that, best to find the faulty equipment and throw it out before it gets worse. I don’t like grounding probes because they can mask issues. Although they could enable a GFCI to trip if there is a fault, rather than your body enabling the GFCI to trip. I still cringe a little bit when I put my hand in the tank after having two stray current issues
A ground probe paired with gfci protection is the one and only way to go. Then the probe won’t ‘mask’ things, and you won’t have to think twice about putting your hands in tank. Safer for you, safer for livestock
 

n2585722

2500 Club Member
View Badges
Joined
Jun 17, 2013
Messages
3,663
Reaction score
2,116
Location
Cedar Park, Tx
Rating - 0%
0   0   0
Man this is frustrating p.o.s. short for positive this really is something else
If you are reading AC there is no positive. There is a hot, neutral and ground. Neutral should be close to ground potential. Ground is added as a safety precaution. You can alway use the + sign for positive next time. The way a GFIC works is the current on the hot side should match the current on the neutral side. If they don't the current must have found another path so it trips. It sounds like you have a metal type heater and the exposed metal case is grounded. That is the same as having a ground probe in the tank.
 

Creating a strong bulwark: Did you consider floor support for your reef tank?

  • I put a major focus on floor support.

    Votes: 38 43.2%
  • I put minimal focus on floor support.

    Votes: 20 22.7%
  • I put no focus on floor support.

    Votes: 28 31.8%
  • Other.

    Votes: 2 2.3%
Back
Top