Is there anyway to pause an alarm? For example, when my ATO level sensor goes off it takes me a day or so to get around to refilling it and during this time I get constant alerts. Is there a way to pause the alarm for specific events like this?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
I would it if there was a convenient way to ignore the alarm trip for a number of hours. I don’t think there is. I manually turn the alarm off in Fusion until I get around to correcting the thing causing the alarm.
How do you manually turn it off in fusion? Thanks
On your Fusion page you have something like the attached image. Move the alarm sliders to off and that will stop audio warnings, emails, texts.
Turning off the alarm output is not a good thing to do. I'll go so far as to say it's a really BAD thing. A good way to handle non-critical alarm conditions is by use of a virtual output. Here is an example for low ATO reservoir:
[ReservoirLow] (a virtual output)
Set OFF
If ResLow OPEN Then ON
If Time 08:01 to 19:59 Then OFF
If Time 20:01 to 07:59 Then OFF
Then test the state of that virtual outlet in the email program:
[EmailAlarm]
{your existing programming}
If Output ReservoirLow = ON Then ON
This assumes that the float switch or optical sensor named ResLow is OPEN when the water level in the reservoir is low. If the water level is low, the VO will only turn on for 1 minute at exactly 8AM and/or 8PM, thereby also only turning on the alarm output for 1 minute twice a day.
Voila! You get a reminder that the ATO reservoir needs to be refilled just twice a day, and at convenient times of your choosing. And this also eliminates the big problem of forgetting to slide the email tile slider from OFF to AUTO. Even more importantly, other much more critical alarms can still come through.