Your Resident Electrician for all your electrical questions!

Taxus812

Destroyer of corals
View Badges
Joined
Mar 28, 2019
Messages
716
Reaction score
788
Location
Windsor
Rating - 0%
0   0   0
Thanks for the help. I am loving this site !! sooooo much better than walking into Home Depot and and asking someone (well trying to figure it out on my own)
 

fishead

Community Member
View Badges
Joined
Dec 27, 2011
Messages
80
Reaction score
49
Location
Australia
Rating - 0%
0   0   0
Hi helpful electricians. I'm looking at back up power options to run my return pump and one of the flow pumps (Red Dragon RD3 50w and a single MP40).
Could I permanently maintain a 130 amp hour AGM 12v battery with a smart charger and run the above pumps from an inverter coming from the battery?
Full time?
With a power outage the two pumps would run off the battery until exhausted. Don't know how long the battery would last with that load but should give me time to start the generator. If just a short outage when power comes back on the smart charger would kick back in and charge the battery. Would the battery have a limited life in that configuration and would there be a significant delay in the battery being able to run things after draining and then restarting the charger??
Am just seeing if I can avoid an auto switching set up really.
Thanking you, Steve.
 

Peace River

Thrive Master
View Badges
Joined
Apr 29, 2014
Messages
21,518
Reaction score
164,618
Location
USA
Rating - 100%
1   0   0
Hi! Do y'all know if there is a plugin adapter (or similar) that I can connect between my canister filter and the wall outlet so that the filter won't come back on when the house loses/regains power? I want something that will force a manual reset and not just automatically restart. I know that the easy answer is don't use a canister filter, but there are times that I use them for temporary tanks and other people ask questions about how to work around the risk of anoxic conditions in the filter created from extended power loss.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
Hi helpful electricians. I'm looking at back up power options to run my return pump and one of the flow pumps (Red Dragon RD3 50w and a single MP40).
Could I permanently maintain a 130 amp hour AGM 12v battery with a smart charger and run the above pumps from an inverter coming from the battery?
Full time?
With a power outage the two pumps would run off the battery until exhausted. Don't know how long the battery would last with that load but should give me time to start the generator. If just a short outage when power comes back on the smart charger would kick back in and charge the battery. Would the battery have a limited life in that configuration and would there be a significant delay in the battery being able to run things after draining and then restarting the charger??
Am just seeing if I can avoid an auto switching set up really.
Thanking you, Steve.
Yes, you could do that. Shouldn't be a problem at all. As for how long it will hold, let assume 100W between the two pumps. 100W @ 12VDC is 8 amps. With 130AH at an 8 amp rate gives you roughly 16 hours.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
Hi! Do y'all know if there is a plugin adapter (or similar) that I can connect between my canister filter and the wall outlet so that the filter won't come back on when the house loses/regains power? I want something that will force a manual reset and not just automatically restart. I know that the easy answer is don't use a canister filter, but there are times that I use them for temporary tanks and other people ask questions about how to work around the risk of anoxic conditions in the filter created from extended power loss.
I don't know of an off the shelf product that would do this.
 

Peace River

Thrive Master
View Badges
Joined
Apr 29, 2014
Messages
21,518
Reaction score
164,618
Location
USA
Rating - 100%
1   0   0
I don't know of an off the shelf product that would do this.
Ok, thanks. I’ll try to build one with an arduino.
 

fishead

Community Member
View Badges
Joined
Dec 27, 2011
Messages
80
Reaction score
49
Location
Australia
Rating - 0%
0   0   0
Yes, you could do that. Shouldn't be a problem at all. As for how long it will hold, let assume 100W between the two pumps. 100W @ 12VDC is 8 amps. With 130AH at an 8 amp rate gives you roughly 16 hours.
Thanks for your help my friend.
 

Peace River

Thrive Master
View Badges
Joined
Apr 29, 2014
Messages
21,518
Reaction score
164,618
Location
USA
Rating - 100%
1   0   0
If you need help, let me know. It can easily be done a relay and a push button.
Thank you, that sounds like a simpler approach. If you can point me in the right direction then I should be able to put it together. Do you have a specific relay and/or switch in mind?
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
Thank you, that sounds like a simpler approach. If you can point me in the right direction then I should be able to put it together. Do you have a specific relay and/or switch in mind?
I don't have a relay in mind, but if you don't see something from my by mid Monday, give me a shout out. I can draw out and scan what you need to do and make a relay and button recommendation.
 

Peace River

Thrive Master
View Badges
Joined
Apr 29, 2014
Messages
21,518
Reaction score
164,618
Location
USA
Rating - 100%
1   0   0
I don't have a relay in mind, but if you don't see something from my by mid Monday, give me a shout out. I can draw out and scan what you need to do and make a relay and button recommendation.
Awesome! Thank you!
 

wareagle

Active Member
View Badges
Joined
Mar 28, 2019
Messages
161
Reaction score
139
Rating - 0%
0   0   0
Hi! Do y'all know if there is a plugin adapter (or similar) that I can connect between my canister filter and the wall outlet so that the filter won't come back on when the house loses/regains power? I want something that will force a manual reset and not just automatically restart. I know that the easy answer is don't use a canister filter, but there are times that I use them for temporary tanks and other people ask questions about how to work around the risk of anoxic conditions in the filter created from extended power loss.
A manual reset GFCI will do this, it has to be reset anytime you lose power, plug it in, or when it trips. Not sure if you want the GFCI part, but it's an option. Link with manual and auto reset GFCI outlets.
http://towermfg.com/gfci-in-line/
 

Peace River

Thrive Master
View Badges
Joined
Apr 29, 2014
Messages
21,518
Reaction score
164,618
Location
USA
Rating - 100%
1   0   0
A manual reset GFCI will do this, it has to be reset anytime you lose power, plug it in, or when it trips. Not sure if you want the GFCI part, but it's an option. Link with manual and auto reset GFCI outlets.
http://towermfg.com/gfci-in-line/
Thank you! This looks like exactly what I wanted, but I didn't know what to ask for. I don't really need the GFCI, but if that is the mechanism that trips the switch then that is fine. Besides, I don't think GFCI is a bad thing in a fish room! @Brew12 's approach will likely be less expensive, but it is nice to know that there is an off-the-shelf option.
 

MSB123

Someone out there put something smart here.
View Badges
Joined
Aug 11, 2017
Messages
3,487
Reaction score
3,431
Location
Santa Barbara, CA
Rating - 0%
0   0   0
Hello Helpful people!
I am getting a new tank and I need to know what electrical I need to run.
I will be replacing the entire panel and running a sub panel, I just need advice on what to do and how to configure it.
Here is a rundown of current equipment and its wattage:
Screen Shot 2019-04-13 at 8.44.55 PM.png
So total of about 10 amps.
The tank is 260 gallons.
I think I should run 4x 15 amp lines. Or should I run 4x 20 amp lines to account for future additions?
Also, what is a good socket array for 8 sockets?

I am thinking 1 socket for each EB832, and then 2 for my return pumps, and the 4 spare.
The first two I would want 4 at 15 amps, the second two at 10 amps, and the remaining ones at 5 amps

Thanks!
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
A manual reset GFCI will do this, it has to be reset anytime you lose power, plug it in, or when it trips. Not sure if you want the GFCI part, but it's an option. Link with manual and auto reset GFCI outlets.
http://towermfg.com/gfci-in-line/
That's a nice find! I didn't think anyone made those anymore.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
Hello Helpful people!
I am getting a new tank and I need to know what electrical I need to run.
I will be replacing the entire panel and running a sub panel, I just need advice on what to do and how to configure it.
Here is a rundown of current equipment and its wattage:
Screen Shot 2019-04-13 at 8.44.55 PM.png
So total of about 10 amps.
The tank is 260 gallons.
I think I should run 4x 15 amp lines. Or should I run 4x 20 amp lines to account for future additions?
Also, what is a good socket array for 8 sockets?

I am thinking 1 socket for each EB832, and then 2 for my return pumps, and the 4 spare.
The first two I would want 4 at 15 amps, the second two at 10 amps, and the remaining ones at 5 amps

Thanks!
I wouldn't bother with more than 4 @ 15A and it is very likely that 2 @ 15A will be more than you ever need.

I'd have a hard time recommending the socket layout without seeing the tank location. The only advice I could offer there is to not put any outlets behind the tank where they are not easily accessed. I have one that I would have to drain and remove my sump if I ever need to change it out. That won't be fun.
 

MSB123

Someone out there put something smart here.
View Badges
Joined
Aug 11, 2017
Messages
3,487
Reaction score
3,431
Location
Santa Barbara, CA
Rating - 0%
0   0   0
The tank will be on the inside of the house bordering an exterior wall. I am drilling through that wall and putting the sump outside so I can have more water volume and space. I am thinking that I will mount the outlet under the stand so that I can run cords from outside through the wall and plug them in inside. I will also have all of my Apex equipment under the standbyThe tank will be on the inside of the house bordering an exterior wall. I am drilling through that wall and putting the sump outside so I can have more water volume and space. I am thinking that I will mount the outlet under the stand so that I can run chords from outside through the wall and plug them in inside. I will also have all of my Apex equipment under the stand
I wouldn't bother with more than 4 @ 15A and it is very likely that 2 @ 15A will be more than you ever need.

I'd have a hard time recommending the socket layout without seeing the tank location. The only advice I could offer there is to not put any outlets behind the tank where they are not easily accessed. I have one that I would have to drain and remove my sump if I ever need to change it out. That won't be fun.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
The tank will be on the inside of the house bordering an exterior wall. I am drilling through that wall and putting the sump outside so I can have more water volume and space. I am thinking that I will mount the outlet under the stand so that I can run cords from outside through the wall and plug them in inside. I will also have all of my Apex equipment under the standbyThe tank will be on the inside of the house bordering an exterior wall. I am drilling through that wall and putting the sump outside so I can have more water volume and space. I am thinking that I will mount the outlet under the stand so that I can run chords from outside through the wall and plug them in inside. I will also have all of my Apex equipment under the stand
With the sump no under the stand you should have plenty of room to change the receptacles if needed. I think it should work fine to put at least 2 of the circuits under the stand. You may want to put a 3rd up higher for the lights, especially if you have a canopy.
 

MSB123

Someone out there put something smart here.
View Badges
Joined
Aug 11, 2017
Messages
3,487
Reaction score
3,431
Location
Santa Barbara, CA
Rating - 0%
0   0   0
With the sump no under the stand you should have plenty of room to change the receptacles if needed. I think it should work fine to put at least 2 of the circuits under the stand. You may want to put a 3rd up higher for the lights, especially if you have a canopy.
The lights will be hanging freely, with the cords routed behind the tank (I bought watertight extension cords.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
The lights will be hanging freely, with the cords routed behind the tank (I bought watertight extension cords.
Forgot you were using T5's, so you will want those on the Apex.
 

High pressure shells: Do you look for signs of stress in the invertebrates in your reef tank?

  • I regularly look for signs of invertebrate stress in my reef tank.

    Votes: 38 32.2%
  • I occasionally look for signs of invertebrate stress in my reef tank.

    Votes: 28 23.7%
  • I rarely look for signs of invertebrate stress in my reef tank.

    Votes: 22 18.6%
  • I never look for signs of invertebrate stress in my reef tank.

    Votes: 30 25.4%
  • Other.

    Votes: 0 0.0%
Back
Top