Hello,

I'm in the midst of having a HVAC mini duct split installed for my aquarium room, but have an electrical question.

My current breaker for the circuit is a double pole 20amp breaker (photo 1).
unnamed.jpg


However, my A/C unit requires the following 230v 1 phase 60 Hz, Max Breaker size 15 amps. (photo 2)

unnamed.png


Currently the only thing running on the circuit is a refrigerator. My questions are:

1). Do I need to replace the 20amp breaker with a double pole 15amp breaker, given the unit shows a Max breaker rating of 15?
2). Can a mini split unit be on the same circuit as the refrigerator or does it have to be on a dedicated circuit?
3). Will the 230V single phase require a 14/3 wire (2 hots) or 14/4 wire?

- Thanks
 

vetteguy53081

Well known Member and monster tank lover
View Badges
Joined
Aug 11, 2013
Messages
91,815
Reaction score
202,725
Location
Wisconsin -
Rating - 100%
13   0   0
Hello,

I'm in the midst of having a HVAC mini duct split installed for my aquarium room, but have an electrical question.

My current breaker for the circuit is a double pole 20amp breaker (photo 1).
unnamed.jpg


However, my A/C unit requires the following 230v 1 phase 60 Hz, Max Breaker size 15 amps. (photo 2)

unnamed.png


Currently the only thing running on the circuit is a refrigerator. My questions are:

1). Do I need to replace the 20amp breaker with a double pole 15amp breaker, given the unit shows a Max breaker rating of 15?
2). Can a mini split unit be on the same circuit as the refrigerator or does it have to be on a dedicated circuit?
3). Will the 230V single phase require a 14/3 wire (2 hots) or 14/4 wire?

- Thanks
@Brew12
 

TriggerCorals

Community Member
View Badges
Joined
Nov 12, 2017
Messages
37
Reaction score
29
Location
Danville
Rating - 0%
0   0   0
1) That breaker in the picture is actually a tandem breaker and can’t be used for 2-pole equipment. Those breakers take up one breaker space and are only on one pole. The. Realer you need per national electric code is like the 40 amp 2-pole above that breaker. You need to have installed by an electrician a 2-pole 15 amp breaker per the HVAC specs.

2) you must run a dedicated 2-pole 15 amp circuit for the unit and cannot share it with anything else. The fridge should also be dedicated ideally.

3) you will require a 14-3 (ground is not counted in NM cable- Romex) 2 hots, 1 neutral, 1 ground. Run to a disconnect and then the the unit itself. Also per code, a regular receptacle outlet is required within six feet of the unit outside.
 

Paul B

10K Club member
View Badges
Joined
Nov 3, 2010
Messages
18,080
Reaction score
61,634
Location
Long Island NY
Rating - 0%
0   0   0
TriggerCorals is exactly correct.. You may have space for that breaker in the panel, but we can't see the whole panel. It is "possible" you already have a cable in that room that can be converted for your needs but only an electrician can tell you that.
Good luck
(Master Electrician 50 years. :beaming-face-with-smiling-eyes: )
 

SoggyNW

Active Member
View Badges
Joined
Apr 9, 2019
Messages
421
Reaction score
627
Location
Wenatchee
Rating - 0%
0   0   0
If your panel is full then your gonna need one of these.

Eaton BQ215240

I'm not positive that is the exact model you need but something like it should be available for your panel. It does the same thing as the tandem breaker but across both phases for 240 v applications.
 

West1

Valuable Member
View Badges
Joined
Jul 26, 2016
Messages
1,945
Reaction score
633
Location
Idaho
Rating - 100%
1   0   0
The scenario
Reefer 525XL RODI top off water in last cabinet compartment and it’s crammed. I’d like to buy the Tunze ATO 3155 switch socket and setup a Brute ATO in my garage, roughly 40’ away and on the same level/surface.

The question
With the link and vid, what wire can I run under my house in the crawl space to connect pump to 3155?

The Idea
I’m going to run a low volume pump (not sure what or size) with approximately .25” Inner Diameter tubing, wrapped in plumbing pipe insulation as close to the floor insulation as possible for winter.

Thanks for the help! Open for suggestions!!

 

Paul B

10K Club member
View Badges
Joined
Nov 3, 2010
Messages
18,080
Reaction score
61,634
Location
Long Island NY
Rating - 0%
0   0   0
Exposed or buried wiring/cable must be listed for its application. Type UF cable is the most commonly used nonmetallic cable for residential outdoor wiring runs.

This is direct burial cable and even though you are not burying it, it is tough stuff and harder for creatures to bit through it. Although they still can.

Here is the code for outdoor wiring. But just go to wherever you buy wire in your area and get UF cable. It looks like Romex but will probably be gray and harder to strip.


Good luck
 

Beau_B

Valuable Member
View Badges
Joined
Jun 29, 2019
Messages
1,532
Reaction score
1,417
Rating - 0%
0   0   0
You don’t need UF. It’s low voltage signal wire, not line, as it requires a receptacle at the pump location. I haven’t looked up the specs but you could likely use bell 18/2 wire. Landscape 16/2 would be another option, which is basically lamp cord.
 

Paul B

10K Club member
View Badges
Joined
Nov 3, 2010
Messages
18,080
Reaction score
61,634
Location
Long Island NY
Rating - 0%
0   0   0
OMG,you may be correct. :beaming-face-with-smiling-eyes: I didn't look at his link. I thought he wanted to put the outlet for the Tunze 40 feet away.
If he is running just the low voltage wires 40' the wiring can not be 18/2 as the voltage drop on DC would not run the pump at any speed.

I am also not sure what this thing does as I never used one. But the video stats that you can also use it to run a 110Volt AC pump in which case you would need to wire according to code.

We would need to know what pump he is using as to watts and volts. If it is 12 volts DC, he "may" need #12 wire.
If it's a dinky little make up water pump, 14/2 may work :)
 

Beau_B

Valuable Member
View Badges
Joined
Jun 29, 2019
Messages
1,532
Reaction score
1,417
Rating - 0%
0   0   0
It’s not powering the pump, it’s just switching the outlet. Just travelers for signal, as I understand it.

likewise would need to read the specs on it, but that’s what I took from the short description
 

Paul B

10K Club member
View Badges
Joined
Nov 3, 2010
Messages
18,080
Reaction score
61,634
Location
Long Island NY
Rating - 0%
0   0   0
I don't know exactly what it is doing. :)
 

WVNed

The fish are staring at me with hungry eyes.
View Badges
Joined
Apr 11, 2018
Messages
10,206
Reaction score
43,620
Location
Hurricane, WV
Rating - 0%
0   0   0
He's pulling in a relay with 12 volts that switches the power from a wall outlet. That let's you run an AC pump with a Tunze ATO.
 

West1

Valuable Member
View Badges
Joined
Jul 26, 2016
Messages
1,945
Reaction score
633
Location
Idaho
Rating - 100%
1   0   0
I was thinking about using my deepwater bldc 5 pump from the garage on lowest setting.

open to other pumps as an option



Deepwater Aquatics Distribution BLDC5 DC Brushless Pump
 

Paul B

10K Club member
View Badges
Joined
Nov 3, 2010
Messages
18,080
Reaction score
61,634
Location
Long Island NY
Rating - 0%
0   0   0
He's pulling in a relay with 12 volts that switches the power from a wall outlet.
So the pump is plugged in somewhere and he just wants to control it from a different location?
 

WVNed

The fish are staring at me with hungry eyes.
View Badges
Joined
Apr 11, 2018
Messages
10,206
Reaction score
43,620
Location
Hurricane, WV
Rating - 0%
0   0   0
So the pump is plugged in somewhere and he just wants to control it from a different location
I think so. You plug the pump into the Tunze device. You plug the device into a wall outlet. The ATO switches the device to turn the pump on and off.
Not sure how far you could extend this low voltage circuit.
 

West1

Valuable Member
View Badges
Joined
Jul 26, 2016
Messages
1,945
Reaction score
633
Location
Idaho
Rating - 100%
1   0   0
I think so. You plug the pump into the Tunze device. You plug the device into a wall outlet. The ATO switches the device to turn the pump on and off.
Not sure how far you could extend this low voltage circuit.

correct, here’s a link to the idea. I’ll also need to use an AC pump (thought I could use a DC).

you bring up a good point on distance for low voltage. Is there a way to test something similar before buying the Tunze Socket?

 

The Farmer

Well-Known Member
View Badges
Joined
Nov 24, 2020
Messages
803
Reaction score
1,337
Location
Michigan
Rating - 0%
0   0   0
16awg speaker wire would work. But I would run it through a conduit to protect the wire from the elements. The speaker wire is a stranded copper wire which makes it more pliable. It can handle up to 14v dc
 

WVNed

The fish are staring at me with hungry eyes.
View Badges
Joined
Apr 11, 2018
Messages
10,206
Reaction score
43,620
Location
Hurricane, WV
Rating - 0%
0   0   0
correct, here’s a link to the idea. I’ll also need to use an AC pump (thought I could use a DC).

you bring up a good point on distance for low voltage. Is there a way to test something similar before buying the Tunze Socket?


With DC you are going to do better with something like speaker wire that is multi stranded and as little electrical resistance as possible.
 

WVNed

The fish are staring at me with hungry eyes.
View Badges
Joined
Apr 11, 2018
Messages
10,206
Reaction score
43,620
Location
Hurricane, WV
Rating - 0%
0   0   0
There used to be a Tunze person on R2R who could probably tell you what you need to know. Not sure how to find them.

Okay Duh
Tunze is a sponsor here and has a sub forum for questions in that section
 
Last edited:

Algae invading algae: Have you had unwanted algae in your good macroalgae?

  • I regularly have unwanted algae in my macroalgae.

    Votes: 45 35.4%
  • I occasionally have unwanted algae in my macroalgae.

    Votes: 28 22.0%
  • I rarely have unwanted algae in my macroalgae.

    Votes: 9 7.1%
  • I never have unwanted algae in my macroalgae.

    Votes: 10 7.9%
  • I don’t have macroalgae.

    Votes: 31 24.4%
  • Other.

    Votes: 4 3.1%
Back
Top