I have been having the darnedest time with this fan program.

Fallback Off
If tmp > 80.9 then on
If tmp < 79.6 then off
Min time 015:00 then on

I want it to come on at 81, stay on at least 15 minutes, and then turn off at 79.5

However it’s currently 79.1 and the fan is still running.

Help?
 

ihavecrabs

2500 Club Member
View Badges
Joined
Nov 25, 2014
Messages
2,792
Reaction score
3,679
Location
Illinois
Rating - 0%
0   0   0
Hello all!

I have been having the darnedest time with this fan program.

Fallback Off
If tmp > 80.9 then on
If tmp < 79.6 then off
Min time 015:00 then on

I want it to come on at 81, stay on at least 15 minutes, and then turn off at 79.5

However it’s currently 79.1 and the fan is still running.

Help?

Try adding "Set OFF" after the fallback command.

#Apexusers
 

ihavecrabs

2500 Club Member
View Badges
Joined
Nov 25, 2014
Messages
2,792
Reaction score
3,679
Location
Illinois
Rating - 0%
0   0   0
Oh and I'm not sure about your min time statement.. I think what it is doing is turning your fan on again after 15 minutes of it turning off. This might be your problem.

If you are looking for it to stay on for a minimum of 15 minutes, I'd use the following command.

Defer 015:00 Then OFF

Add it after the ON command
 
OP
OP
Bill_Moorman

Bill_Moorman

Active Member
View Badges
Joined
Jun 14, 2018
Messages
277
Reaction score
327
Location
Pueblo, Colorado
Rating - 0%
0   0   0
So something like:

Fallback OFF
Set OFF
If Tmp > 80.9 Then ON
Defer 015:00 Then OFF
If Tmp < 79.6 Then OFF

Does that look right?
 

ihavecrabs

2500 Club Member
View Badges
Joined
Nov 25, 2014
Messages
2,792
Reaction score
3,679
Location
Illinois
Rating - 0%
0   0   0
So something like:

Fallback OFF
Set OFF
If Tmp > 80.9 Then ON
Defer 015:00 Then OFF
If Tmp < 79.6 Then OFF

Does that look right?

Yes..

However, now that I think about it, based on the order it is in, it may turn off after 15 minutes without getting down to 79.6, but will turn back on again when it gets above 80.9.

Is that what you were looking for.
 
OP
OP
Bill_Moorman

Bill_Moorman

Active Member
View Badges
Joined
Jun 14, 2018
Messages
277
Reaction score
327
Location
Pueblo, Colorado
Rating - 0%
0   0   0
I just am trying to prevent it from cycling on and off giving around a half degree. Not sure the best way to go about it!
 

Pezking182

Community Member
View Badges
Joined
Jul 22, 2018
Messages
91
Reaction score
120
Location
Taunton MA
Rating - 0%
0   0   0
You can prevent cycling by setting a dead band. So...

if tmp > 80 + . 5 then on
If tmp < 80 - . 5 then off

In this case your target would be 80 and the temp would be allowed to drift +-0.5deg. If it was above 80.6 it would turn on until it dropped below 79.6

You could also add an or statement like...

If tmp < 79.6 or min time >015:00 then off

This would shut off the fan if either condition is true.

I dont know what controller this is as I dont have one. But I am a control engineer and write code for commercial building automation systems. Generally anticycling is done with a minimum off duration, not a minimum run time, but I understand why you want want minimum run time. Also, programs will execute the last command given. So in your case,
Min time 015:00 then on will execute and turn the fan back on.

Again, just my .2 cents
 

Drauka99

Active Member
View Badges
Joined
Nov 19, 2015
Messages
364
Reaction score
156
Location
Northwest Florida
Rating - 0%
0   0   0
So something like:

Fallback OFF
Set OFF
If Tmp > 80.9 Then ON
Defer 015:00 Then OFF
If Tmp < 79.6 Then OFF

Does that look right?


I would replace the Defer line with the Min time like you had the first time, So:

Fallback OFF
Set OFF
If Tmp > 80.9 Then ON
Min time 015:00 then ON
If Tmp < 79.6 Then OFF

that should do as you want. The fan will run of a minimum of 15 minutes when it is triggered.

IMO, The defer command likely works but Defer is more to "defer" a command for a time to ensure a state BEFORE something is triggered, like a float switch bouncing between open and closed.
 

Sleepydoc

Valuable Member
View Badges
Joined
Apr 10, 2017
Messages
1,423
Reaction score
1,266
Location
Minneapolis, MN
Rating - 0%
0   0   0
You're trying to use min time and defer to avoid rapid cycling of the fan, but you already have a hysteresis built into your program by having the on temp 1.3º higher than the off temp. There's no way your tank will cool down by 1.3º in less than 15 minutes, but if it did, you wouldn't necessarily want the fans to keep going and drive the temp down further.

Also, adding the 'set OFF' statement defeats the hysteresis.

You should be able to use:

Fallback OFF
If Tmp > 80.9 then ON
If Tmp < 79.6 then OFF
 

SuncrestReef

That Apex guy
View Badges
Joined
Jan 18, 2018
Messages
4,214
Reaction score
9,217
Location
Oregon
Rating - 0%
0   0   0
This is what I use for my fan. The Defer commands turn it on once the temp reads 78.2 for at least 15 seconds, and stays on until the temperature reads 78.0 for at least 15 seconds. I've found it runs for about 7 - 10 minutes roughly once or twice per hour and maintains the temperature between 78.2 - 77.9, which isn't much of a noise nuisance.

Fallback OFF
Set OFF
If Tmp > 78.1 Then ON
If Tmp < 78.1 Then OFF
Defer 000:15 Then ON
Defer 000:15 Then OFF
 

Creating a strong bulwark: Did you consider floor support for your reef tank?

  • I put a major focus on floor support.

    Votes: 59 39.9%
  • I put minimal focus on floor support.

    Votes: 33 22.3%
  • I put no focus on floor support.

    Votes: 50 33.8%
  • Other.

    Votes: 6 4.1%
Back
Top