Apex have been shutting off the co2 when the ph not reached

David Cher

Well-Known Member
View Badges
Joined
Feb 8, 2016
Messages
851
Reaction score
156
Rating - 0%
0   0   0
anyone can help ?

below is the program i set on the co2 plug

Fallback OFF
Set OFF
If pHCR > 7.00 Then ON
If pHCR < 6.90 Then OFF

SCreenshot.jpg
 

Diesel

ME=1, CANCER=0.
View Badges
Joined
Apr 14, 2012
Messages
13,613
Reaction score
16,449
Location
Katy
Rating - 0%
0   0   0
Try it this way,

Fallback ON
If PHCR > 7.00 Then ON
If PHCR < 6.65 Then OFF

Btw, I have it set at 6.65 and so must you as most CaRx media will not melt 100% if the PH doesn't reach a PH in the reactor below 6.70
 

dcmartinpc

Active Member
View Badges
Joined
Jan 22, 2009
Messages
337
Reaction score
402
Rating - 0%
0   0   0
Correct. Set OFF tells the apex that the default state of the outlet is off unless something changes that state. So when the pH is greater than 7 it turns on the outlet, then it turns on the co2, drops the pH to 6.99 and turns the outlet off since that is the default state.
 

dcmartinpc

Active Member
View Badges
Joined
Jan 22, 2009
Messages
337
Reaction score
402
Rating - 0%
0   0   0
Fallback ON can be very dangerous if the energy bar loses communication with the Apex if you are relying on the Apex to control the solenoid. If that happens it can keep dumping co2 and seriously drop the pH in your reactor and melt the media if your regulator has issues. In my experience, these problems always seem to happen at the exact same time!
 