That's elexactly what I'm trying to figure out. You tell meWell if you give me a day I can tell you how much weight per square inch/foot that floor system can carry and what size tank may work for you, of course that number gets affected by furniture, flooring type, type(if any) of finish material on garage ceiling, etc.
Thank You thIs Is More Of What I Was Looking For. A definite no. Lol. I was thinking of going with a 120 but idk if that would even be worth doing. .I work for an architectural firm (commercial mainly), in addition I have done extensive structural work for a shoring company. I went to school for mechanical engineering.
The floor above the garage, assuming that the house was built in accordance with the current codes, will be designed for either a 20 psf load (attic w/ storage), 30 psf (habitable attic with fixed stairs) or the best case scenarios a room at 40 psf. Your tank will be approx 4,000 pounds distributed over 24 square feet or so which is 167 psf. with a best case scenario of spanning across 6 trusses.
I don't even have to run calcs to come to the following conclusion. Your trusses will not support your aquarium without reinforcing. There are a lot of options on how this can be accomplished, all of them requiring a structural engineer. I recommend hiring someone local, let me know if you would like further assistance and good luck.
Jason
I agree it would be if there is a remote chance of being possible.My 180G cost me about $5000 to setup, I imagine a 400G would be a fair bit more. If I was in the same spot as you, an additional $400-600 consultation would be worth every penny.
I work for an architectural firm (commercial mainly), in addition I have done extensive structural work for a shoring company. I went to school for mechanical engineering.
The floor above the garage, assuming that the house was built in accordance with the current codes, will be designed for either a 20 psf load (attic w/ storage), 30 psf (habitable attic with fixed stairs) or the best case scenarios a room at 40 psf. Your tank will be approx 4,000 pounds distributed over 24 square feet or so which is 167 psf. with a best case scenario of spanning across 6 trusses.
I don't even have to run calcs to come to the following conclusion. Your trusses will not support your aquarium without reinforcing. There are a lot of options on how this can be accomplished, all of them requiring a structural engineer. I recommend hiring someone local, let me know if you would like further assistance and good luck.
Jason
Ive never heard of anyone verifying the floor load on a water bed haha. (I grew up having those).
A king size water bed is roughly 6 1/2 ' x 6 1/2 ' for a total of 42 square feet or so therefore the load is distributed over a nice wide area. At 200 gallong gallons of water or so, plus the weight of the bed and the water at 8.4 lbs / gallon is 1,680 lbs or so for a total uniform load of 40 psf, (plus the bed) so roughly 42 psf. While this is just a bit over the standard required design loads of flooring it certainly within all safety factors and most floor designs are already designed to hold more weight that code requirements.
Another factor (in comparison to the original situation) is the span and that in most homes the joists run in the short direction.
Lentz, if you want to take some pictures i can point out what dimensions are needed and i can run it past one of our structural engineers to see if you're at least in the ballpark.
What kind of pictures do you want.Ive never heard of anyone verifying the floor load on a water bed haha. (I grew up having those).
A king size water bed is roughly 6 1/2 ' x 6 1/2 ' for a total of 42 square feet or so therefore the load is distributed over a nice wide area. At 200 gallong gallons of water or so, plus the weight of the bed and the water at 8.4 lbs / gallon is 1,680 lbs or so for a total uniform load of 40 psf, (plus the bed) so roughly 42 psf. While this is just a bit over the standard required design loads of flooring it certainly within all safety factors and most floor designs are already designed to hold more weight that code requirements.
Another factor (in comparison to the original situation) is the span and that in most homes the joists run in the short direction.
Lentz, if you want to take some pictures i can point out what dimensions are needed and i can run it past one of our structural engineers to see if you're at least in the ballpark.
Correct me if I'm wrong, but if there were 2-200lb fish in a tank they are going to displace quite a bit of water weight (on the floor if you didn't account for it ;-). 2-200lb loads on a waterbed wouldn't displace any weight just add that much more load onto the floor. just put a bunch of fat guys up on your second floor and toss a milky way into the pile, if the floor holds up you're likely good to go.Well, most 400gallon aquariums don't have 200lb fish and for customers buying king size water beds you often have 2 of those big fish and they sometimes, you know, make the water move a lot more than the mp60s (not sure how many psf that is ) .... Of course they don't stay on the bed 24/7 but 8 hours a day good be a good guess. All that need to be taking into consideration right?????