Hi there,

I have a large RO reservoir that I only want to refill if the low level sensor is activated. The high level sensor will cut power to the solenoid. This is the programming I currently have:

Fallback OFF
If ATO_lo OPEN Then ON
If ATO_hi CLOSED Then OFF

The issue I'm having is that whenever the water level in the reservoir drops below the ATO_hi sensor (anytime the ATO pump pumps enough water out), the solenoid kicks on and refills the bin. It's not waiting until the water level drops to the ATO_lo sensor. Is there some code I'm missing?

I'm using the newer MOS Optical Sensors from Neptune.
 

Coolcasino

Well-Known Member
View Badges
Joined
Apr 29, 2020
Messages
729
Reaction score
344
Rating - 0%
0   0   0
Try this...

Fallback OFF
If ATO_hi CLOSED Then OFF
If ATO_lo OPEN Then ON
Defer 000:05 Then OFF
 

braaap

Valuable Member
View Badges
Joined
Jul 16, 2015
Messages
2,482
Reaction score
2,734
Location
Montana
Rating - 100%
3   0   0
Fallback OFF
Set OFF
If ATO_hi CLOSED Then OFF
If ATO_lo OPEN Then ON
 

TOP 10 Trending Threads

HOW DO YOU ADJUST YOUR CUC AS ALGAE DISAPPEARS?

  • Capture and re-home CUC

    Votes: 7 7.1%
  • Increase white light/hours in tank to spur algae growth to feed CUC

    Votes: 6 6.1%
  • Feed nori to support CUC

    Votes: 35 35.4%
  • Feed herbivore pellets to support CUC

    Votes: 33 33.3%
  • Allow attrition to balance CUC and algae

    Votes: 43 43.4%
  • Provide macro algae to feed CUC

    Votes: 6 6.1%
  • Introduce CUC predators

    Votes: 1 1.0%
  • Other (please explain)

    Votes: 11 11.1%
Back
Top