Discussion in 'Do It Yourself (DIY)' started by skinz78, Feb 8, 2011.

How to wire a GFCI outlet

  1. skinz78

    skinz78 Moderator Staff Member Team R2R R2R Supporter R2R Excellence Award

    Joined:
    May 8, 2009
    Messages:
    21,867
    Likes Received:
    211
    Location:
    lovely rainy NW Washington
    Disclaimer.
    I am a licensed electrician, my way of doing electrical work is just my interpretation of the National Electrical Code and what I feel is good workmanship. Every electrician has their own interpretation of the code and in some cases do electrical work in other ways than I do. I am not saying my way is the only way, but it is how I have done it for eleven years now.
    The most important thing to remember when doing electrical work is to make very good connections. Loose wires cause fires. This is no joke just a plain fact, that should be written in the Bible. :angel:The second most important thing to do is make sure all power is turned off before working on anything. Getting shocked sucks, believe me.

    OK now that I am done with my rant I will do a step by step explanation on how to wire a GFCI with outlets protected by it down stream. : FIRST THINGS FIRST, disconnect all power.

    The visual difference between a GFCI and a standard outlet, the GFCI is on the left.
    [​IMG]

    Now you can wire one GFCI up so it protects all other outlets downstream of it. Or you can just buy a GFCI for every outlet you want protected. It is cheaper to buy one GFCI and then protect each outlet downstream but it is a little more complicated to do it that way. I am not a prices guy but I think the GFCI's are about $10 ea compared to a buck or two for normal outlets. I am going to show you how to do it with one GFCI protecting other outlets in this thread.
    GFCI's have two spots to put sets of wires in them, they are labeled LINE and LOAD. In this pic you will see LINE on the right side and LOAD on the left side.
    [​IMG]

    GFCI's need the power coming in to them to be on the LINE side of the outlet and whatever it is to protect downstream of the GFCI hooks to the LOAD side. Just remember the LOAD is what the GFCI is driving. Sorry my pic on the right the wording is cut off. It says power from panel.
    [​IMG]

    Now I have ran the wire in between the two boxes and in this picture you can see the wire coming into the box. But more importantly you can see the yellow outer shield "sheathing" of the wire. This pic is to demonstrate the proper amount of sheathing to be in the box. On the left you can see I have about 3/8" of sheathing in the box and on the right you can see I have about 1 1/4" of sheathing in there. This is a minimum and maximum amount. Also for stapling you don't want to staple too hard, just enough to hold the wire in place without cutting into the sheathing.
    [​IMG]

    Now you will have black, white, and a bare or green ground wire. Now assuming your house is wired correctly, the black wire is almost always your power or positive wire. The white wire is almost always your neutral or negative wire, and the bare or green is your ground. On most GFCI brands you can usually put 2 power and 2 neutral LINE wires to the outlet. There should also be spots to put 2 power and 2 neutral LOAD wires to the outlet. But there is only one spot to attach the ground wire to the GFCI so you will need to wire nut them all together with a single "pigtail" to attach to the GFCI. I take and push all the ground wires down into the bottom corner of the box so they are all grouped together.
    [​IMG]

    Then trim them all the same length about 2" out of the box. Next take a scrap of ground wire "approx 12 inches or longer" and wire nut it in with the wires coming out of the box. Once this is done neatly fold the wire nut and the wires back into the box.
    [​IMG]

    Next I take the set "black and white" that I know is my LINE "power coming from the panel" and gently twist them up to mark them as different than the others.
    [​IMG]

    At this point you are ready to fold and cut all the wires to final length. I fold them all to the bottom and to the back as neatly as possible. Then I place my hand on them to measure, all you need is one hand length coming out of the box.
    [​IMG]

    Next strip all the wires about 3/4" long, but I leave some of the wrap on the LINE wire.
    [​IMG]

    You are now ready to connect the wires to the GFCI. Remember it is important to keep your LINE and LOAD separate and hook them where they are labeled to go. One other way to know where where the power and neutral wire go's is that the silver screw is the neutral and the gold is the power. Notice no visible copper wire is showing, this is what you want. Exposed can short out.
    [​IMG]

    Finally you can neatly as possible fold the wire back into the box thus pushing the GFCI into the box as well. make sure your bare ground wire isn't touching any of the white or black screws or bare copper.
    [​IMG]

    OK now screw in the GFCI and put the plate on and installation is complete.

    Next I am going to show you how to install a 2 gang or quad outlet. Basically it is 4 spots to plug into in one box. You will need a 2 gang box for this. In my application I have a wire in and a wire out to the next outlet. Now remember these are all on the LOAD side of the GFCI and are protected.
    One major difference in this application is you will need two ground wires, one for each outlet. In this pic I have the two ground pigtails and I have take one set of black and white wires and trimmed them to hand length. The second set of black and white wires I leave long.
    [​IMG]

    The long wires I strip at hand length and wrap it around the outlet screw. This leaves a long pigtail coming off of the screw. This pigtail later connects to the second outlet. Sort of a jumper. Notice I have my wires wrapped tightly to the screws and going clockwise so when I tighten the screw it pulls the wire under it instead of pushing it out.
    [​IMG]

    Once all connections are made to the first outlet you can screw it into the box. Then you will have the single ground, one long black and one long white wire left over. Push them into the back and bottom of the box and cut them hand length.
    [​IMG]

    Then connect the second outlet up and screw it into the box, add your cover plate then you should be done.
    [​IMG]

    Turn your breaker back on and reset the GFCI, you should then have power to all your outlets.:smile:

    If you have any questions please feel free to ask!

    Ok one last final rant :sad:
    You need GFCI outlets, plain and simple with no exceptions. There is a lot of debate on this. Some people say well what if you aren't home and the GFCI trips. My response to that is what if you are working on your tank with your arm in the water while standing in a puddle and the water comes in contact with the electrical outlet. Simple, the GFCI trips. Now imagine the same scenario but with no GFCI protection and lets throw in a heart condition that you didn't know about. What happens is you get shocked, the electricity takes the quickest path to ground which just happens to be through your body to the wet puddle you are standing in. The electricity flows through your body and in doing so passes through your heart causing it to cease to beat. Now what is a bigger problem, your heart beat stopping or you take doing a full on nuke caused by a tripped GFCI while you were away? I do realize I just threw a lot of what if's out there but I truly feel I don't want the chance of a what if to happen to me, do you?
     
    Last edited by a moderator: May 2, 2017
    Fishnerd7, andy71, Behnken and 9 others like this.
    Tags:

  2. Wy Renegade

    Wy Renegade Zs and Ps/PE collector R2R Supporter R2R Excellence Award

    Joined:
    Feb 5, 2009
    Messages:
    3,780
    Likes Received:
    64
    Location:
    Wyoming
    Nice thread Chris and great post on the wiring! Another alternative for those who aren't as handy as others is to consider a power strip with a true GFCI breaker built in. Not a surge protector like you would buy for a computer, but a true GFCI that works just like the outlet above.

    I believe these Belkin ones are now discontinued, but there are other brands of these available;

    [​IMG]

    Please be aware that the coralife timer strips DO NOT have a GFCI built in to them, and this is what happens when they make contact with saltwater;

    [​IMG]

    In this particular case, a GFCI may have saved $100.00s of dollars in tank equipment, including several powerheads as well as the light and labor to replace a fried breaker. Fortunately, nobody was hurt.

    Having a GFCI not only protects your life and your livestock, it also protects your equipment.
     
    JP79, Thoms_here and Daniel Bodily like this.
  3. skinz78

    skinz78 Moderator Staff Member Team R2R R2R Supporter R2R Excellence Award

    Joined:
    May 8, 2009
    Messages:
    21,867
    Likes Received:
    211
    Location:
    lovely rainy NW Washington
    Good point, I have also used one of the GFCI powerstrips on my old tank because I couldn't get to the outlet after the tank was set to replace it with a GFCI.

    That is scary on the Coralife timer, I use one for my lighting... But it is GFCI protected and is on the top of my aquarium hood well away from the water.
     
  4. Wy Renegade

    Wy Renegade Zs and Ps/PE collector R2R Supporter R2R Excellence Award

    Joined:
    Feb 5, 2009
    Messages:
    3,780
    Likes Received:
    64
    Location:
    Wyoming
    I have the same problem on my 65gal, thats why I hunted that belkin down a few years ago.

    On the timer, this particular one was supposed to be up on a ledge, well away from the water. But, somebody had knocked it down and they overfilled the tank slightly. The overspill happened to land on the timer strip - snap, crackle, fizzle, and the lights went out and the power along the entire back side of the building shut down. Fortunately the tank/timer was sitting on a countertop so nobody was standing in the puddle of water.
     
  5. mdb_talon

    mdb_talon Well-Known Member

    Joined:
    Dec 6, 2010
    Messages:
    163
    Likes Received:
    12
    Location:
    ofallon
    I previously used powerstrips with built in GFCI on a tank and every single time the power would go out for even a second it would trip the GFCI when power came back on. I tried two seperate strips (different types/brands) and it was the same problem. Finally after a day the tank went without power (due to a blip where we only probably lost power a few seconds) I wired a GFCI receptacle to the fish tank in question. Never had issues like that since. I dont have any idea if my experience with the strips was unlucky or uncommon, but just wanted to throw it out there.
     
  6. Wy Renegade

    Wy Renegade Zs and Ps/PE collector R2R Supporter R2R Excellence Award

    Joined:
    Feb 5, 2009
    Messages:
    3,780
    Likes Received:
    64
    Location:
    Wyoming
    mdb I've never had any issues with my belkin kicking back on without throwing the GFCI due to power outages, but I can't speak to any of the other brands.
     
  7. fsu1dolfan

    fsu1dolfan Well-Known Member R2R Supporter

    Joined:
    May 9, 2008
    Messages:
    2,642
    Likes Received:
    16
    Location:
    South Florida
    Skinz - Great writeup and pics...i have been meaning to switch my current outlets to GFCI. Maybe ill get some motivation to do it soon.
     
  8. Reef Breeders

    Reef Breeders The LED Guy R2R Supporter Gold Sponsor Toys For Kids 2016

    Joined:
    Dec 21, 2010
    Messages:
    3,712
    Likes Received:
    99
    Location:
    Shelton CT
    I hate gfcis, they are verrrrry picky. You cant just piggy back a wire on the load side, you NEED a line and load. IE, if the outlet goes out, anything on the line end also goes out. It will not turn on unless it is wired that way.
     
  9. greg0385

    greg0385 Well-Known Member

    Joined:
    Jan 23, 2011
    Messages:
    1,324
    Likes Received:
    9
    Location:
    summertown,tn
    great thread, brings back memories of electrical schooling (i took that i never used). if im not mistaken(which i may be) all houses now have to have these and i want to say they want to have AFCI's(Arc Fault something something) too....... might have to break out my NEC code book to read up on that again.
     
    xREEFINaintEZx likes this.
  10. Reef Breeders

    Reef Breeders The LED Guy R2R Supporter Gold Sponsor Toys For Kids 2016

    Joined:
    Dec 21, 2010
    Messages:
    3,712
    Likes Received:
    99
    Location:
    Shelton CT
    Only near water, like in kitchens and baths
     
  11. nixer

    nixer Well-Known Member

    Joined:
    Apr 27, 2010
    Messages:
    1,320
    Likes Received:
    2
    Location:
    indiana
    not always. there are some state, county, and town codes that require them in garages or anything subgrade. im sure there has to be somewhere that requires them in the entire house.
     
  12. skinz78

    skinz78 Moderator Staff Member Team R2R R2R Supporter R2R Excellence Award

    Joined:
    May 8, 2009
    Messages:
    21,867
    Likes Received:
    211
    Location:
    lovely rainy NW Washington
    The NEC requires any outlets within 6' of a sink, all kitchen outlets, all bath outlets, all outside outlets, all garage outlets including the door opener, and all crawlspace outlets.
     
  13. mikezalewski

    mikezalewski Well-Known Member

    Joined:
    May 11, 2011
    Messages:
    67
    Likes Received:
    0
    Location:
    michigan
    This is a good DIY posting because this is where the complete system starts from and ends with if not careful. The one thing to make this better is the idea that you can also talk to the electrical employees in Home Depot or Lowes and ask them how to wire this up they can usually help as well!
     
  14. iprayforwaves

    iprayforwaves Active Member

    Joined:
    Jul 18, 2011
    Messages:
    26
    Likes Received:
    0
    Location:
    Orlando, FL
    Run all my tanks with GFI Outlets, thought I'm not electrically capable enough to wire them up myself. Very informative post!
     
  15. Acipenser

    Acipenser Member

    Joined:
    Feb 17, 2012
    Messages:
    13
    Likes Received:
    1
    Location:
    Georgia
    I am not an electrician - so please check with one before doing any of this yourself.
    You can also wire multiple GFCI outlets so that they will only trip the individual set of outlets where the fault occurred.

    Personally I prefer this method, as one faulty piece of equipment does not shut down the whole series of outlets. It is more expensive, but it allows me to isolate the individual fault and keep the rest of the outlets running. This can only be done with multiple GFCI outlets. Normal outlets will not offer any protection down the line.

    This can be done by daisy chaining the outlets off the line side of the outlet. Power goes into the line side of one outlet, and out the line side of the same outlet to the line side of the next outlet. Very similar to the original post, just don't use the load side.
     
    andy71 likes this.
  16. skinz78

    skinz78 Moderator Staff Member Team R2R R2R Supporter R2R Excellence Award

    Joined:
    May 8, 2009
    Messages:
    21,867
    Likes Received:
    211
    Location:
    lovely rainy NW Washington
    Yes you are correct, I have 4 of them set up that way on my 120g tank.
     
  17. Mike&Terry

    Mike&Terry Wrasses, Angels, & Tangs, Oh My! Staff Member Team R2R R2R Supporter R2R Excellence Award Reef Spotlight Award Photo of the Month Award Article Contributor

    Joined:
    Oct 7, 2011
    Messages:
    6,084
    Likes Received:
    1,406
    Location:
    Chesterfield, VA
    Great thread Chris!
    There are so many excellent tips in here for the DIY'er. I always prefer to use the screws for making connections to outlets versus using backstab connections. Depending on the quality of the outlets, and the gauge wire being used, those backstab connections can cause problems, IME.
     
  18. redtop03

    redtop03 Well-Known Member R2R Supporter Gold Sponsor

    Joined:
    Oct 12, 2009
    Messages:
    965
    Likes Received:
    4
    Location:
    Barbourville Ky.
    +1...the push in connection on the back only has a tiny flat piece that bites into the wire and is very prone to loosing connection after the copper wire has aged/tarnished,using the screws is a much better idea
     
  19. skinz78

    skinz78 Moderator Staff Member Team R2R R2R Supporter R2R Excellence Award

    Joined:
    May 8, 2009
    Messages:
    21,867
    Likes Received:
    211
    Location:
    lovely rainy NW Washington
    I am an electrician and you wouldn't believe how many service calls I get because people use the stab in type outlets... Money in my pockets LOL!
     
  20. Reef Breeders

    Reef Breeders The LED Guy R2R Supporter Gold Sponsor Toys For Kids 2016

    Joined:
    Dec 21, 2010
    Messages:
    3,712
    Likes Received:
    99
    Location:
    Shelton CT
    LOL those things always fail, I am phasing them out of my house gradually, whenever I run a new line for a light, outlet, etc. I re do the outlet, the wires rip out just by working in the box.
     