Still struggling with programming my APEX ATO. Currently it has topped off past the upper and lower optic sensors creating an alarm. Is there something wrong with my output program?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
This^ in addition, verify the opticals show the correct state of CLOSED = covered with water, OPEN = above water after checking they are seated properly and set to optical in the FMM module setup.Your code looks good. Here's mine. The extra lines are not need.
Fallback OFF
Set OFF
If Sump_L OPEN Then ON
If Sump_H CLOSED Then OFF
If Res_Lo OPEN Then OFF
Defer 000:30 Then ON
Defer 000:15 Then OFF
When On > 005:00 Then OFF
Min Time 030:00 Then OFF
Also check your sensors are clean and seated into the fmm all the way. Also in the fmm mine has change from optical to flow.
Do you see anything wrong with my email alarms?This^ in addition, verify the opticals show the correct state of CLOSED = covered with water, OPEN = above water after checking they are seated properly and set to optical in the FMM module setup.
When testing, you can temporarily remove the Min Time line so you don't have to wait 30 minutes between tests and then add it back once you have verified it is functioning properly.
You don't want line 4 or 7 at all. Delete those.
So I have Error AUTO TOPOFF in line three. Will that cover any issues with the topoff that I need to be aware of?You don't want line 4 or 7 at all. Delete those.
It tells you the most important one. The if Error tells you if the pump tried to run longer than the When Statement duration and was latched off to manual OFF. If/when that happens, you can investigate why and set the pump back to auto if all looks good.So I have Error AUTO TOPOFF in line three. Will that cover any issues with the topoff that I need to be aware of?
I’m trying to figure out why my ATO has started filling my sump up to and beyond the optical sensors. Is it possible the label I put on the outside of the sump, it was directly across from the sensors, interfered with them.It tells you the most important one. The if Error tells you if the pump tried to run longer than the When Statement duration and was latched off to manual OFF. If/when that happens, you can investigate why and set the pump back to auto if all looks good.
The issue this won't notify you for is if the ATO hasn't ran for a while because the optical sensor is dirty. That can be done using a virtual output like this
LowSump
Set OFF
If ATOlow CLOSED Then ON
Defer 300:00 Then ON
Email add
If Output LowSump = ON Then ON
Where you put the label is where it should fill to once everything is tested and working properly.I’m trying to figure out why my ATO has started filling my sump up to and beyond the optical sensors. Is it possible the label I put on the outside of the sump, it was directly across from the sensors, interfered with them.