Tanks are, obviously, a potentially wet environment. For wet environments, it's important to have GFCI outlets/breakers to protect against shocks on the circuit your tank is on.

However, I was thinking - a battery backup or UPS blocks the ability for the GFCI breaker to protect you.

Say you have a spill that causes a short. The GFCI detects this and shuts down power to the circuit. If you have a UPS on that circuit for your tank, that UPS would think there's been a power outage, and supply power with its battery... meaning you could potentially still be dead despite the GFCI having done its job.

So, are UPS something we should even have? I have one, and it's been great during power outages... but is it worth the risk?
 

Jamie814

Well-Known Member
View Badges
Joined
Mar 15, 2021
Messages
930
Reaction score
751
Location
IOWA
Rating - 100%
6   0   0
So, are UPS something we should even have? I have one, and it's been great during power outages... but is it worth the risk?
Yes, still a valuable tool for power outages. A GFCI cord after the UPS will solve this issue. Power cords with them built in are readily available.

Something like this,
GFCI Extension Cord
 

fryman

Active Member
View Badges
Joined
Dec 28, 2020
Messages
489
Reaction score
474
Location
Belmont
Rating - 0%
0   0   0
Since almost all our equipment is DC nowadays, battery backup is best handled DC-DC. If you use a traditional UPS, you are converting DC from the battery to AC, then using an AC-DC convertor to power the equipment. Very inefficient, and also more expensive. I recommend using a LiFePO4 battery and DC-DC converters.

A well-designed battery system should have fuses installed.

I use a fuse at the battery positive terminal like this: BOJACK MRBF 50A, 58V DC Terminal

and for each positive wire, sized appropriately something like this:
Anyongora 16AWG Inline Fuse
 
Last edited:

MaPePo

New Member
View Badges
Joined
Jan 16, 2026
Messages
24
Reaction score
8
Location
USA
Rating - 0%
0   0   0
So, are UPS something we should even have? I have one, and it's been great during power outages... but is it worth the risk?
Yes, still a valuable tool for power outages. A GFCI cord after the UPS will solve this issue. Power cords with them built in are readily available.

Something like this,
GFCI Extension Cord
After as in Wall GFCI -> UPS -> GFCI Extension cord -> tank controller?
 

BeanAnimal

7500 Club Member
View Badges
Joined
Jul 16, 2009
Messages
9,274
Reaction score
15,565
Rating - 0%
0   0   0
Yes, still a valuable tool for power outages. A GFCI cord after the UPS will solve this issue. Power cords with them built in are readily available.

Something like this,
GFCI Extension Cord
Actually it will not. The UPS is a floating neutral. So in theory the hot wire has no reference to earth ground. You can still get shocked between hot and neutral coming from the UPS, but you are the load, and even if you are grounded. The GFCI will not read the fault.
 

BeanAnimal

7500 Club Member
View Badges
Joined
Jul 16, 2009
Messages
9,274
Reaction score
15,565
Rating - 0%
0   0   0
After as in Wall GFCI -> UPS -> GFCI Extension cord -> tank controller?
As noted above, due to the floating neutral, the GFCI will NOT work as expected on the output side of a typical home or small business UPS that is running on battery. That said, if the fault occurs while running on mains, then the GFCI dow stream of the UPS will function and trip.
 
Last edited:

Pistondog

5000 Club Member
View Badges
Joined
Jun 28, 2020
Messages
6,054
Reaction score
9,977
Rating - 0%
0   0   0
Actually it will not. The UPS is a floating neutral. So in theory the hot wire has no reference to earth ground. You can still get shocked between hot and neutral coming from the UPS, but you are the load, and even if you are grounded. The GFCI will not read the fault.
I think a gfci works by comparing current flow thru hot and neutral, if these dont match by some milliamps, it trips. Gfci should work on floating neutral and even ungrounded systems.
 

BeanAnimal

7500 Club Member
View Badges
Joined
Jul 16, 2009
Messages
9,274
Reaction score
15,565
Rating - 0%
0   0   0
I think a gfci works by comparing current flow thru hot and neutral, if these dont match by some milliamps, it trips. Gfci should work on floating neutral and even ungrounded systems.

Yes, the GFCI works by comparing current on the hot and neutral conductors. The issue is that neutral is not referenced to ground in a floating neutral system.

In a bonded system (neutral to ground) the GFCI protects you any time you are grounded and receive a shock from a GFCI protected circuit, as the current "leaks" or "faults" to ground, even if that shock is from hot -> neutral contact (you are the load). Of course if you make contact with the hot and neutral and are NOT grounded, you get shocked because you are the load and there is no fault.

In the floating system a fault that puts you between hot and neutral of the UPS is not protected by the GFCI, even if YOU are grounded.

On the other hand (don't try this) the hot from the UPS will not shock you if you get between it and ground because it is not referenced to ground.

The bottom line, you can't count on the GFCI to work as intended on a floating neutral system. I hope that makes sense.
 

TOP 10 Trending Threads

WHAT AMOUNT OF LIVE ROCK AND SAND SHOULD BE PRIORITIZED FOR OPTIMAL BIODIVERSITY/FILTRATION?

  • 100% live rock + bagged sand

    Votes: 34 27.0%
  • 100% dry rock + 100% live sand

    Votes: 45 35.7%
  • 50/50 live/dry rock, 50/50 live/bagged sand

    Votes: 27 21.4%
  • 75% live rock, 25% live sand

    Votes: 11 8.7%
  • 25% live rock, 75% live sand

    Votes: 9 7.1%
Back
Top