GFCI tripping

chansman

Community Member
View Badges
Joined
Jul 24, 2012
Messages
66
Reaction score
1
Location
Central South Carolina
Rating - 0%
0   0   0
I installed a GFCI for the 75g that was set-up over the weekend and it trips when I plug in one of the ballasts. The ballast works fine when not on the GFCI...could it just be sensitive? tia
 

kgross

Local Fish Store Owner
View Badges
Joined
Jan 15, 2008
Messages
115
Reaction score
0
Location
Nampa Idaho
Rating - 0%
0   0   0
There could be a problem with the ballast, cap going bad, ignitor going bad etc, or just a sensitive GFCI. Lighting ballasts are known for causing false trips on GFCI breakers.
 

robert

Valuable Member
View Badges
Joined
Jun 14, 2011
Messages
1,028
Reaction score
487
Location
Silicon Valley - Ca
Rating - 0%
0   0   0
+1 Kgross

inductive load - knocks voltage and current out of phase - especially on magnetic ballasts and motors or when the starter cap has gone bad. GFCI sees the in-rush current but the return current is delayed enough to trip the circuit.
 
Last edited:

Reef Breeders

ReefBreeders.com
View Badges
Joined
Dec 21, 2010
Messages
4,681
Reaction score
1,008
Location
North Kingstown, RI
Rating - 0%
0   0   0
I would put a non-gfi outlet next to it, you can simply run it off of the "line" terminal, anything run off of the "load" terminal will also be gfi protected. I know the 20amp gfis have 2 terminals for wires on each screw, except the ground, which you need to twist and crimp. Is it a 1-gang, or 2-gang box?
 
OP
OP
C

chansman

Community Member
View Badges
Joined
Jul 24, 2012
Messages
66
Reaction score
1
Location
Central South Carolina
Rating - 0%
0   0   0
Just a one gang. I have to keep everything neat and tidy or the Mrs. will not be happy. My plan is to take the canopy down today, while rearranging rock, so I'll make sure there is nothing loose.
 
OP
OP
C

chansman

Community Member
View Badges
Joined
Jul 24, 2012
Messages
66
Reaction score
1
Location
Central South Carolina
Rating - 0%
0   0   0
I ran an extension cord over...she hasn't noticed yet...lol! Honestly I have owned the aquarium for 1 week and haven't been able to run the actinic lights...WOW!! I have been jipping myself...that flower anemone is awesome.
 

Akira

Community Member
View Badges
Joined
Jul 25, 2012
Messages
27
Reaction score
3
Location
Utah
Rating - 0%
0   0   0
Also on a side note , do you know if this a 20 amp circuit or a 15 amp? GFCI outlets are also rated for the ampacity of the wire of the circuit they are connected too. 12 awg wire is 20 amps while 14 awg is 15 amps. (using a 20 amp gfci on a 15 amp not recommended and also against code)It has been several years since I was in the electrical field but if my memory serves me correctly there is a slightly more expensive outlet that has a Slow trip on it to compensate for motor start ups etc , this may be a simple solution while still keeping the over current protection next to your tank not the primary panel.
 

Dowtish

5000 Club Member
View Badges
Joined
May 30, 2011
Messages
7,043
Reaction score
85
Location
Murfreesboro TN
Rating - 0%
0   0   0
I personally dont understand why you would want to risk having your GFCI trip at any time on something that could cause a major crash to your system.
 

Young Frankenstein

I sniff ozone and relax.
View Badges
Joined
May 25, 2008
Messages
1,153
Reaction score
135
Location
South Miami
Rating - 0%
0   0   0
+1 Kgross

inductive load - knocks voltage and current out of phase - especially on magnetic ballasts and motors or when the starter cap has gone bad. GFCI sees the in-rush current but the return current is delayed enough to trip the circuit.
Agreed +1
 

Mike&Terry

Wrasses, Angels, & Tangs, Oh My!
View Badges
Joined
Oct 7, 2011
Messages
6,124
Reaction score
1,753
Location
Chesterfield, VA
Rating - 0%
0   0   0
I personally dont understand why you would want to risk having your GFCI trip at any time on something that could cause a major crash to your system.

GFCI are mandatory in the NEC, and across the globe for many applications. The number of mandatory applications are expanding too, from what I read. The simple reason is that they save lives. It only takes 100ma to cause heart fibrillation. I don't see why you wouldn't want to have everything connected to your aquarium protected by GFCI.

As to why there would be nuisance tripping - it is true that inductive loads cause temporary imbalance on the hot/neutral and will trip a GFCI, a properly working unit should NOT cause nuisance tripping (either the load device or the GFCI is probably bad). Good advice is given in this thread about checking startup capacitors. The purpose of those is to even out current/voltage differences on startup of those devices like pumps and ballasts. If the device is designed properly, and the startup caps are within tolerance, the device shouldn't be tripping a properly-functioning GFCI outlet.
 

Young Frankenstein

I sniff ozone and relax.
View Badges
Joined
May 25, 2008
Messages
1,153
Reaction score
135
Location
South Miami
Rating - 0%
0   0   0
GFCI are mandatory in the NEC, and across the globe for many applications. The number of mandatory applications are expanding too, from what I read. The simple reason is that they save lives. It only takes 100ma to cause heart fibrillation. I don't see why you wouldn't want to have everything connected to your aquarium protected by GFCI.

As to why there would be nuisance tripping - it is true that inductive loads cause temporary imbalance on the hot/neutral and will trip a GFCI, a properly working unit should NOT cause nuisance tripping (either the load device or the GFCI is probably bad). Good advice is given in this thread about checking startup capacitors. The purpose of those is to even out current/voltage differences on startup of those devices like pumps and ballasts. If the device is designed properly, and the startup caps are within tolerance, the device shouldn't be tripping a properly-functioning GFCI outlet.
In a perfect world yes :) and agreed they save lives and NEC requires them. Understand also that they are not 100% effective on duing what they are made for. I dont use them for the main circulation pumps.
 

kgross

Local Fish Store Owner
View Badges
Joined
Jan 15, 2008
Messages
115
Reaction score
0
Location
Nampa Idaho
Rating - 0%
0   0   0
Yes a GFCI can save your life, but they can also kill your tank off. The best thing is to use multiple ones so if you have a false trip you don't loose all power to your tank.
 

CJO

Valuable Member
View Badges
Joined
Jun 15, 2010
Messages
2,400
Reaction score
197
Location
Charlotte, NC
Rating - 0%
0   0   0
I had a GFCI breaker that kept tripping the lights in my basement. I replaced the breaker and it's been fine ever since. I've read that they become more (too) sensitive over time.

CJ
 

Akira

Community Member
View Badges
Joined
Jul 25, 2012
Messages
27
Reaction score
3
Location
Utah
Rating - 0%
0   0   0
OK this is to CJO , the breaker that was tripping is an "arc-Fault breaker" not a gfi breaker , its part of the new code for NEC that was established around 2004. But it gets long to explain it all . So while GFI's are great they are'nt designed for higher ampacity load that we tend to put on them with the start up up pumps lights etc while we already have an existing load on them . Thus the question I asked before is it a 15 amp circuit. If you want a cheap fix make the single gang box a 2 gang and install 2 gfi's , 1 for pumps and 1 for lighting. Ever tried to run a vacum off a 15 amp gfi ? Try that with a nerw high amp vacum and it will trip same as hair dryer , thats what new NEC code requires a 20 amp circuit and gfi in all bathrooms to handle the higher amperage of the more mondern appliances. When a small amp motor starts up it will draw almost 1.3-1.8 the rated amps and then decrease after its running so seperating pumps and lighting should keep the independant gfi's from tripping . Hope this helps.
 

CJO

Valuable Member
View Badges
Joined
Jun 15, 2010
Messages
2,400
Reaction score
197
Location
Charlotte, NC
Rating - 0%
0   0   0
Thanks for the explanation, Akira. You are correct. I went back and looked and in my case it was an arc-fault breaker.

CJ
 

Akira

Community Member
View Badges
Joined
Jul 25, 2012
Messages
27
Reaction score
3
Location
Utah
Rating - 0%
0   0   0
Your welcome CJ :smile: Just trying to shed a little light on what a "GFCI" actually is and what their intended use is and why they behave as they do.
 

TOP 10 Trending Threads

HOW DO YOU ADJUST YOUR CUC AS ALGAE DISAPPEARS?

  • Capture and re-home CUC

    Votes: 8 7.3%
  • Increase white light/hours in tank to spur algae growth to feed CUC

    Votes: 6 5.5%
  • Feed nori to support CUC

    Votes: 39 35.5%
  • Feed herbivore pellets to support CUC

    Votes: 39 35.5%
  • Allow attrition to balance CUC and algae

    Votes: 46 41.8%
  • Provide macro algae to feed CUC

    Votes: 7 6.4%
  • Introduce CUC predators

    Votes: 1 0.9%
  • Other (please explain)

    Votes: 11 10.0%
Back
Top