We will solve this - I ask some questions to you in
this thread but I can ask the same here
Your setting now
It will give these on and off points. Off at 77.8 F and on at 76.5 again
However - the first thing you need to control is if the rancho temp probe and the GHL probe read the same temperature. Let your rancho operate without putting it into the GHL switch. When the rancho turn the heater off - note the temperature on your GHL Let us say that your GHL shows 78.8 degree F (26 degree C) when your Ranco turn off the heather (The important thing is what GHL thinks the temperature is - not the one you set your Ranco controller at - because it is two different probes and they can differ among themselves !) Now you want your fail safe be at GHL temperature of 79.7 degree F (26.5 degree C) and temperature should go down to 78.8 before the outlet is switching on again - you can test this. Nominal value 79,5 and Hysteresis 1.4 F.
If you press the button in red - you will get this information below. Heather function is switched off at 79.7 F and on again at 78.8. It means that when GHL think it is 78.8 it will switch on the outlet and give power to the ranco controller again. If the ranco is defect and stuck at on - the temperature will rise to 79.7 again and GHL will switch the outlet off. If the ranco is working the right way - the temperature will go down to ranco´s lower on point and off at 78,8 again by the ranco controller. GHL will not shout it down before it reach 79.7 again.
Now you should knit this temp 1 (in my case) to your outlet (SW1 in my case)
Now you can put your Ranco into SW1 and it should work the way it is intended
Sincerely Lasse