I am going to build a 12V battery backup that will be connected to two MP60's and my Apex (just the 12V power to the Apex head unit). The goal is to keep oxygenation going for 24+ hours in my absence. Apparently the MP60's draw about 12W each at minimum speed. The Apex is 8W or less.

I believe everyone is connecting their equipment with a single common positive and a single common negative. But I noticed a lead-acid battery charger will reach 14-15 volts during charging, so the devices would also be seeing this increased voltage.

1. Does the charging voltage being over 12V cause any problems for the Apex or the Vortechs?

2. Does the Apex draw current through the 12V power supply if an EB8 is energized (normal conditions)? If yes, will this wear out my battery or my battery maintainer?

3. These are my tentative equipment choices. Thoughts?

Noco Genius 5A charger/maintainer


100Ah SLA battery

Thank you
 

KStatefan

2500 Club Member
View Badges
Joined
Jun 24, 2015
Messages
4,143
Reaction score
4,014
Location
MHK
Rating - 0%
0   0   0
I use a voltage regulator in my setup for the part that goes to my controller(GHL). The part that goes to my powerheads (Tunze)is not regulated.

Have you looked at a LiFePO4 system instead of the lead acid?
 

YOYOYOReefer

Valuable Member
View Badges
Joined
Dec 9, 2021
Messages
1,337
Reaction score
925
Location
bloomington il
Rating - 0%
0   0   0
i use a solar charge controller to charge my 400AH battery bank it also has backup to land based power and in worse case it turns on a generator. no issues with any 12 volt appliances, nothing is really 12v, should be called 14 volt. My pumps and equipment all hook to 120 volt coming off the sine wave inverter which runs off the batterys.. . If your backup power is set up right should be no isssues.
 

Brian_68

Well-Known Member
View Badges
Joined
Jul 5, 2019
Messages
707
Reaction score
728
Rating - 0%
0   0   0
Yes, will need a 12 V DC to 120 V AC inverter to power the APEX / pumps. Don't forget the draw of the converters themselves as they can be significant and are not anywhere near 100% efficient depending on what is chosen. If the pump uses 12 watts it will be more than that coming from the battery.
 

Spieg

Valuable Member
View Badges
Joined
Jan 12, 2020
Messages
1,424
Reaction score
1,429
Rating - 0%
0   0   0
MP60s run on DC... no need to convert to AC and then back to DC again (this would be a tremendous waste of battery power).
 

RobB'z Reef

2500 Club Member
View Badges
Joined
Apr 23, 2020
Messages
2,783
Reaction score
5,773
Location
Eau Claire
Rating - 0%
0   0   0
I'd seriously consider lifepo4. Yes it's a slightly higher initial investment but lead acid is ancient garbage. It'll work, but not for very long (2-3 years vs 5-10) and at a much higher capacity over time. A good pure sine wave converter should be about 97% efficient. You can build a system to go straight to the battery with everything and skip the power bricks but adding in fuses and possibly step ups when needed for 24v just increases complexity. But maybe that's ok too. An MPP with an inverter makes everything pretty awesome, safe and automated but it's a steep investment. A good ones I'd recommend is from MPP Solar. You should be able to run your pumps with the difference while charging without an issue.
 

Jenuvio

Active Member
View Badges
Joined
Feb 20, 2020
Messages
218
Reaction score
283
Location
Ventura County
Rating - 100%
1   0   0
its called an inverter, for the intended use, make sure to get a sine wave inverter.
Yes. Make sure to get a pure sine wave. I have my lights and powerheads running on solar and one of my pumps failed due to using a modified sine wave. Note that a modified sine wave inverter will work but it shortens the life of your equipment if constanty running.
 

Brian_68

Well-Known Member
View Badges
Joined
Jul 5, 2019
Messages
707
Reaction score
728
Rating - 0%
0   0   0
I'd seriously consider lifepo4. Yes it's a slightly higher initial investment but lead acid is ancient garbage. It'll work, but not for very long (2-3 years vs 5-10) and at a much higher capacity over time. A good pure sine wave converter should be about 97% efficient. You can build a system to go straight to the battery with everything and skip the power bricks but adding in fuses and possibly step ups when needed for 24v just increases complexity. But maybe that's ok too. An MPP with an inverter makes everything pretty awesome, safe and automated but it's a steep investment. A good ones I'd recommend is from MPP Solar. You should be able to run your pumps with the difference while charging without an issue.
They are only that 97% efficient if pulling a decent load typically 30-50% of rated and a specified type of load. Use a 500w inverter and only pull 5% (25w) the efficiency drops to 75% or even 50% in actual testing. Standby with no load is a killer for battery drain.



1642637043931.png
 

Attachments

  • 1642636953835.png
    1642636953835.png
    102.6 KB · Views: 48

BZOFIQ

2500 Club Member
View Badges
Joined
Jul 31, 2014
Messages
4,690
Reaction score
3,990
Location
NYC
Rating - 100%
9   0   0
Yes, will need a 12 V DC to 120 V AC inverter to power the APEX / pumps. Don't forget the draw of the converters themselves as they can be significant and are not anywhere near 100% efficient depending on what is chosen. If the pump uses 12 watts it will be more than that coming from the battery.

its called an inverter, for the intended use, make sure to get a sine wave inverter.


Absolutely NOT!. There is no point to convert it down to 12V DC to upconvert to 120V AC to downconvert it back to 12V. That's insane.

You need a power supply/charger to both supply power to your device and charge battery. In the event of a power loss you can power your pumps/apex directly from the battery.
 
Last edited:

DWill

Active Member
View Badges
Joined
Jan 11, 2020
Messages
444
Reaction score
375
Rating - 0%
0   0   0
Use LiFe batteries and solar to charge them at least as a backup. I have my all my pumps running of off solar and LiFe batteries. Power from the house is the backup. The backup to all of that is a small generator that will run my return pump, heaters and my refrigerator and a couple lamps in the house.
 

BZOFIQ

2500 Club Member
View Badges
Joined
Jul 31, 2014
Messages
4,690
Reaction score
3,990
Location
NYC
Rating - 100%
9   0   0
I did exactly what the O/P is trying to do with both the 12 & 24V outputs. The Idea is to provide power and provide battery backup to DC Pumps and Powerheads along with apex and couple of other things using industrial power supplies and modules. These things are designed to operate in critical environments with quality far exceeding what is provided with your hobby grade equipment.

1642638885200.png


Here is my setup, not all completed in this picture as I dont have anything recent. It doesnt have to be this elaborate at all.

I setup similar for a friend of mine but on a much simpler scale. 2 SLA batteries, 10 Amp P/S, UPS Module and a DC Breaker.

Look at post #26 in this thread for some ideas. In addition to what I posted there you'll need 24V to 12V converter. These things can easily be found on ebay.

 

RobB'z Reef

2500 Club Member
View Badges
Joined
Apr 23, 2020
Messages
2,783
Reaction score
5,773
Location
Eau Claire
Rating - 0%
0   0   0
They are only that 97% efficient if pulling a decent load typically 30-50% of rated and a specified type of load. Use a 500w inverter and only pull 5% (25w) the efficiency drops to 75% or even 50% in actual testing. Standby with no load is a killer for battery drain.



1642637043931.png
That's a good point thank you!
 

ConectadoNZ

Community Member
View Badges
Joined
Sep 25, 2019
Messages
46
Reaction score
19
Location
New Zealand
Rating - 0%
0   0   0
I went with PO4lithium battery and I do power 2 MP40s, plus Vectra S2 using their fuse cable and the booster for the Vectra! When you add from the battery to the Ecotech controller that will be converted as my understanding so it’s all working as intended…
2D7B396F-5856-4135-8A61-EC9CBB45BED0.jpeg
 

Attachments

  • 01D2CC75-DE4F-4ADC-A2D7-5BB28D7DBE65.jpeg
    01D2CC75-DE4F-4ADC-A2D7-5BB28D7DBE65.jpeg
    213.6 KB · Views: 53

High pressure shells: Do you look for signs of stress in the invertebrates in your reef tank?

  • I regularly look for signs of invertebrate stress in my reef tank.

    Votes: 42 31.6%
  • I occasionally look for signs of invertebrate stress in my reef tank.

    Votes: 30 22.6%
  • I rarely look for signs of invertebrate stress in my reef tank.

    Votes: 27 20.3%
  • I never look for signs of invertebrate stress in my reef tank.

    Votes: 34 25.6%
  • Other.

    Votes: 0 0.0%
Back
Top