I'm planning to install a 1200 W UPS (2 x 12 V 9 Ah batteries) to feed the return pump and may be the Profilux controller of my reef tank. The return pump is a Royal Exclusiv RD3 60 W model. Any experience on how much time such a UPS might feed the return pump working at 50-100% power.

Thank you
 

laverda

2500 Club Member
View Badges
Joined
Jun 6, 2008
Messages
2,893
Reaction score
2,165
Location
Anaheim
Rating - 0%
0   0   0
I don't know the specific answer. I do know that motors and some electronics can be fussy and require full sine wave out put from the UPS to run properly. Most UPS less than 1500 do not produce full sign wave output.
 
OP
OP
chema

chema

Active Member
View Badges
Joined
May 14, 2016
Messages
362
Reaction score
295
Location
Salamanca (Spain)
Rating - 0%
0   0   0
I don't know the specific answer. I do know that motors and some electronics can be fussy and require full sine wave out put from the UPS to run properly. Most UPS less than 1500 do not produce full sign wave output.

I agree with you in the problem related to the sine wave. That may be solved by using a battery backup of the right voltage, instead of a UPS. The problem is that the RD3 can not be connected to a battery, only to its own controller. Or at least I do not know how to do it.
 

srobertb

Well-Known Member
View Badges
Joined
Jun 16, 2021
Messages
986
Reaction score
1,065
Location
SE Texas
Rating - 0%
0   0   0
I use a COR pump and have my Apex entirely on a sine wave UPS. It works just fine. Granted it runs about 3x a year for an hour max.

I can run everything but heater, lights, and xf350’s for 1.5 hours.
 

cristiano frade

New Member
View Badges
Joined
Jun 22, 2021
Messages
3
Reaction score
2
Location
Brazil
Rating - 0%
0   0   0
If your pump is DC (I believe it is) you dont need a full sine wave, and here how to calculate how many hours it will last:
1 - your batteries have total energy of 2 x 12v x 9AH = 216 VAh.
2 - your pumps consumes 60w (V x A)
3 - considering your UPS has 80% efficiency (typical), you will have 216 x 0,8 / 60 = 2,88 hours. This is considering that you will run your pump at maximum power.

Only AC pumps require full sine wave fyi.
 
OP
OP
chema

chema

Active Member
View Badges
Joined
May 14, 2016
Messages
362
Reaction score
295
Location
Salamanca (Spain)
Rating - 0%
0   0   0
If your pump is DC (I believe it is) you dont need a full sine wave, and here how to calculate how many hours it will last:
1 - your batteries have total energy of 2 x 12v x 9AH = 216 VAh.
2 - your pumps consumes 60w (V x A)
3 - considering your UPS has 80% efficiency (typical), you will have 216 x 0,8 / 60 = 2,88 hours. This is considering that you will run your pump at maximum power.

Only AC pumps require full sine wave fyi.
Thanks for the calculations. However, the RD3 is an AC adjustable pump, so a full sine wave UPS is required.
 

KStatefan

2500 Club Member
View Badges
Joined
Jun 24, 2015
Messages
4,134
Reaction score
4,009
Location
MHK
Rating - 0%
0   0   0
You can not use all of the 9AH in the battery only 50 - 80% depending on the type of battery
 

Algae invading algae: Have you had unwanted algae in your good macroalgae?

  • I regularly have unwanted algae in my macroalgae.

    Votes: 45 35.4%
  • I occasionally have unwanted algae in my macroalgae.

    Votes: 28 22.0%
  • I rarely have unwanted algae in my macroalgae.

    Votes: 9 7.1%
  • I never have unwanted algae in my macroalgae.

    Votes: 10 7.9%
  • I don’t have macroalgae.

    Votes: 31 24.4%
  • Other.

    Votes: 4 3.1%
Back
Top