If the tank outlet is protected by the bathroom gfci read the rating on it to see if it is 15 amp or 20 amp. Then find out which breaker in your electric panel turns off that outlet and see if it is 15 or 20 amp. If the breaker is 20 amp (and the wire connected to it is 12 gauge) you can use a 20 amp gfci outlet.
None of this is needed.
There is no difference between the capability of a 15A or 20A standard or GFCI receptacle. The 15A receptacle is rated for a 20A branch circuit, its only difference is the style of plug that can be used with it. There is nothing in the aquarium world that (at least applicable here) that would have a NEMA 20P plug.
If the living room outlets are protected by the bathroom gfci i would re-wire the gfci so it only protects itself and nothing outside of the bathroom and add another gfci outlet in the first outlet box in the living room so each outlet has less load.
This would be better handled by an electrician, and if he were doing that, then it would be best to replace all of the receptacles that serve the fish tank with GFCIs. This reduces single points of failure.
Something to consider is that there may be other receptacles in the living room that are not on the same circuit. I would want to have those GFCI protected as well. But that is outside the scope of the question.
Even better than that would be a gfci breaker in the panel for those outlets. If you install a gfci breaker in the panel the outlet in the bathroom can be changed to a standard outlet.
The issue here is twofold.
1) By code, the breaker upgrade would trigger the requirement that the breaker meet current code, which in under most AHJs means the breaker MUST be AFCI. So a combo AFCI/GFCI breaker would need to be used.
2) this puts all of the eggs back on one basket and creates a single point of failure.
So my take would be to have an electrician install the AFCI breaker and downstream GFCIs.
NOTE on why a single GFCI receptacle or breaker creates issues"
Many devices do leak tiny amounts of current. The scale of each devices leaks are below the GFCIs leakage current threshold. But when you plug in numerous devices together, their leakage currents add together. The sum total of all of them can often near or exceed the GFCIs trip threshold. So you end up with intermittent nuisance trips. Nothing is wrong, other than say your lights and heater kicking on at the same time pushes the leakage temporarily over the threshold and the GFCI trips .