Running dry for too long
I get that error when my pump runs dry and it takes long to cover the sensor, you said dripping? It should be a lil jet of water
Is it a jet of water coming out ? Or slow drip like ? Make sure the line to the pump is secure mine sometimes when I move the pump around gets loose
Sounds like something is either not fitted correctly or pump is bad, try taking everything apart and connect it back up if it’s weak sounds more like the lines are not fitted well, this has also happened to me after running it dry I have to stop and start it a few times before the pump starts moving water again
Pump is not working right. It took to long to cover the sensor so it sends an error.
General errors like that are the reason I have every error on a virtual outlet so I know exactly what and why the error was sent.
It depends.
Only real way to tell is to let it do it's thing and see if the pump is pumping water. If there is a nice jet of water coming out, and not just a trickle, the pump is fine, and it may have been a one time issue(something in the pump perhaps stopping it from pumping as hard as it can). If the pump is pumping fine, and you get the error, then the sensor is bad.
So the pump worked when I got it, but now when I try to just over ride it and turn the pump on it doesn’t work? I turn the pump ON in fusion and it does not turn on?
Any advice?
Thanks
So the pump worked when I got it, but now when I try to just over ride it and turn the pump on it doesn’t work? I turn the pump ON in fusion and it does not turn on?
Any advice?
Thanks
Where is the power supply to the FMM plugged into? Not the aquabus cable.
Power supply for the pump is plugged into an outlet on the EB832.
The Error_ATK alert is for anytime the pump has run too long.
Things to check:
-Float Valve is not limiting flow from the PMUP into the tank (had this happen on a friend's tank, the float valve actually has adjustable positions, if it is set too low it will close and not allow the water to pump into the tank)
-Increase run time for ATK (if it is taking to long to cover sensor do this by increasing the When On > time )
-Decrease time in between ATK turning on (do this my decreasing the Min Time line)