You close to the ocean? Ya it’s time for a new panel.It’s in the garage. Not outside.
Very old system.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
You close to the ocean? Ya it’s time for a new panel.It’s in the garage. Not outside.
Very old system.
Have them verify no voltage on the ground. I've seen grounds used as nuetral, junctioned in a light switch box cause similar issues. That panel is a mess but doesn't look that bad for a older fl house. The posts look good/ clean and if it's just 2 circuits, replacing the panel will likely not fix the problem.( if it was the panel, they can simply move the breaker to that empty space). If each circuit shuts off(shows 0vac), with its respective breaker, the issue is almost certainly a nuetral to ground issue. Just make sure he checks... if he sees 109v on a ground, it is very likely someone connected nuetral to ground in a box somewhere. Very possibly in a room next to an addition.Here are the photos he took of our panels
![]()
![]()
![]()
![]()
Can you tell me what I should ask them to do? I’m a little bit confused. Anyway, the supervisor is coming tomorrow and we will discuss exactly what needs to be done. The more info I have to tell them what to do, the better.
Thanks! I just screenshot your post and I’ll show it to the supervisor tomorrow. I really appreciate it.A
Have them verify no voltage on the ground. I've seen grounds used as nuetral, junctioned in a light switch box cause similar issues. That panel is a mess but doesn't look that bad for an older fl house. The posts look good/ clean and if it's just 2 circuits, replacing the panel will likely not fix the problem.( if it was the panel, they can simply move the breaker to that empty space). If each circuit shuts off(shows 0vac), with its respective breaker, the issue is almost certainly a nuetral to ground issue. Just make sure he checks... if he sees 109v on a ground, it is very likely someone connected nuetral to ground in a box somewhere. Very possibly in a room next to an addition.
Wow. Super neat setup. I’ll show your post as well to them. I appreciate it very much!You panel is bit crusty and not the neatest job, but not terrible. Hard to tell what is actually oxidized sometimes without actually getting into it though.
I don't commonly see double (parallel) feeders. I suppose they did it because the smaller gauge wire is easier to pull. But most lugs are not rated for double termination
From NEC:
For a 200A service, using parallel 100A conductors (in compliance with NEC 310.10(G)) is permitted if all the following are true:
Not something that I would worry about one way or the other, I just find it odd, but maybe it is common in that area.
- Conductors are the same length, material, size, and insulation type.
- They terminate in lugs rated for parallel use or double conductors.
- Neutral and ground conductors are also paralleled in the same manner.
So aside from a bit of wire mess, it is hard to tell what is actually bad, but a new panel is cheap. It is the labor that is going to be expensive, as are AFCI and GFCI breakers. But you will be safer in the long run.
My panel... I put it in ~20 years ago. Still fairy neat, all things considered. There is a 80a sub nearby as well (kitchen) and a 100A in the shed.. and yes I have that many circuits
![]()
Prior to late 90's --- many 220V appliances used leg to ground to run the 120V panel lights... YEP they got away with using the ECG as neutral because back then most 220V appliances were only fed L1, L2 and ECG, as no neutral was needed.A
Have them verify no voltage on the ground. I've seen grounds used as nuetral, junctioned in a light switch box cause similar issues. That panel is a mess but doesn't look that bad for a older fl house. The posts look good/ clean and if it's just 2 circuits, replacing the panel will likely not fix the problem.( if it was the panel, they can simply move the breaker to that empty space). If each circuit shuts off(shows 0vac), with its respective breaker, the issue is almost certainly a nuetral to ground issue. Just make sure he checks... if he sees 109v on a ground, it is very likely someone connected nuetral to ground in a box somewhere. Very possibly in a room next to an addition.
Right, and it becomes a problem if, for example, they need another circuit for a added on room(or whatever reason); and only have a 14/2 romex to that corner of the house. Then use the black and white as seperate hots and the ground as nuetral(like 220v). If they're really stupid, both breakers on the same leg of panel. If any of this happened, the issue will persist after replacing the panel. My concern is that if it's old enough, permitting a new panel will require a complete re wire. Of coarse, if it's all new, it will work; but is that what's actually required(?).Prior to late 90's --- many 220V appliances used leg to ground to run the 120V panel lights... YEP they got away with using the ECG as neutral because back then most 220V appliances were only fed L1, L2 and ECG, as no neutral was needed.
Wow. Super neat setup. I’ll show your post as well to them. I appreciate it very much!i
I think most areas require it even if they’re still enforcing older NEC editions. AFCI has been in the code since around 2008 and has expanded with nearly every revision since.
GFCI requirements are pre 2000 for sure and expanded significantly since then, to almost universal by maybe 2018. I would bet most AHJs in Florida are already enforcing at least 2020, if not 2023.
Before anyone asks...
Yes, I read the NEC to keep up to date with each code revision and what is new, and yes, I read the NFPA ratification documents and the arguments for and against each revision. I actually find the justifications and debates oddly fascinating. Sadly, most of that technical back and forth is now paywalled.
It’s really not that neat. That is 20 years of wires being pulled in and out. Most of my panels are a lot cleaner.
It honesty bothers the snot out of me.It is pretty neat for having changes over the years. I really had trouble keeping my neat when I added my garage 50 amp sub and Geothermeal 100 amp sub and it is not has neat as yours.
My brothers service entrance cable was split on the back side. I have never seen so much water run through a panel in heavy rain. It was like a waterfall. I didn't believe him when he tried to explain it to me. It took two or three rains to figure out what the heck was going on. Oddly, never tripped a breaker, but sure was one of those "wow, that is scary" things that you don't see often.Common problem is moisture buildup or rain enters box. I bet your tank is on the bottom breakers. If you open your panel you will probably see water. This occurs when the wire is no longer sealed from outside to inside .
I can't see it from here, so Maybe.He says the breaker panel needs to be changed,
It means the voltage is a little to low for that device. Your electrician needs to check the input voltage and it may vary through the day. If it gets lower than 108 volts, you need to call the power company and they will put a timed meter on your line. For free.What does the caution sign mean on the apex?
Basically, the breaker panel had 3 different wiring in one switch (I’m totally butchering the explanation, he’s sending the full report soon) This makes no sense to me.He said he can’t just create a new outlet because it will be too much power drawn out.
Yes, you can't wire GFCIs together.All the GFCI below the tank are interconnected which makes them basically wired into each other = bad job
Does this electrician have English as his first language? I am having a hard time trying to figure out what he is saying.After my Inspection I notice that the circuits are not independent and they only griping went the 2 circuits are working, the circuits have GFCI concrete serial and these is part of the problem too.
The 2 circuits are in deferents lines and these generate the tripping because in some point of the wiring the 2 lines touch each other.
I replace one circuit and now the 2 circuits are in the same line and know they don’t trip but they have voltage problems.
Part of the problem is the breakers are to old and lose and the final solution is run 2 new circuits because the outlets are Behind the tank piping and not accessible.
Sloppy, and I would have fired the guy if he worked for me, but it is serviceable and can be repaired.Here are the photos he took of our panels
I would remove those feeders (large wires), clean the cable ends and the terminals and put "penetrox" on them before re assembly. It's just some gray stuff that prevents corrosion. I use it on everything including my car terminals and used it extensively on my job as a commercial, industrial construction electrician in Manhattan.Can you tell me what I should ask them to do?
It is weird to see parallel feeders in a house but it will work fine. I don't know the codes in Miami.I don't commonly see double (parallel) feeders. I suppose they did it because the smaller gauge wire is easier to pull. But most lugs are not rated for double termination
Yes, you can't wire GFCIs together.
What is this magic penetrox you use in NY and why have I never been given a tube?I also live on the water and corrosion is a big problem so penetrox should be used. Sometimes it is called
"Anti Ox". It is not normally needed for copper cables, but near the water it is a big help. I use it on everything.