Is there anyway I can use the logic functions within the Profilix 4 to set this up?

I want my eheim jaeger heater, which is hooked up to switch socket 5, to shut off in the case that my GHL flow sensor reads zero flow.

I want to do this because my heater is installed inline within a pvc contraption. Although I have recently redone my plumbing to make sure the heater doesnt run dry in this event, I dont want to risk heating the pvc pipe up to the point of it bending the pipe.

Any experienced people with the GHL logic? I cant make heads or tails of it and the last time I went fiddling around I almost crashed my tank by overdosing alkalinity solution.
 

Ditto

Valuable Member
View Badges
Joined
Apr 25, 2017
Messages
2,229
Reaction score
2,970
Location
Albany, NY
Rating - 0%
0   0   0
@sntmods - Not based on the flow dropping, it in the wish list on there forums.

But I always think outside the box with these type of questions also :)

1- We could use the general alarm, but in turn the heater would turn off not just if the flow turned 0, but if any general alarm came up (Like a PABCOM Error)
2- Program a virtual temp probe with different settings, that would trigger (Would be a lower temp) because the tank temp dropped, because water stop flowing through the PVC contraption?

@Vinny@GHLUSA , @Marco@GHLUSA , @Lasse @WWIII any idea also?
 

Lasse

10K Club member
View Badges
Joined
Mar 20, 2016
Messages
10,830
Reaction score
29,794
Location
Källarliden 14 D Bohus, Sweden
Rating - 0%
0   0   0
Now I´m on unsure ground because I do not have any flow meter to do experiment with. This may be just a fairy tale or the worlds greatest work around :)

But fact - the flow meter works through (in some way) the level input. You have to assign your flow meter to a level input.

At the level inputs - you have a state indicator.

Screen Shot 02-02-19 at 10.35 AM.PNG

I do not know how this will react to the alarm level on the flowmeter - but if they have used this state indicator in order to have alarms for the flow indicator - I supose you can do a work around. Is rather easy to test this. Configure a alarm level on your flow meter. Run the flow and switch of the flow and observe the state indicator. If it changes you can do a work around. Set up a control circuit as a virtual auto top off. Let it use the same level sensor as your flow meter. Now you have to figure out how to use the invert function but the general idea is that you should use a PL function for the socket that manage your heater. The PL should be Temperatur x increase AND Fill water (ATO only) y (y is the number your constructed virtual control circuit) You have to test if you need to use inverted function or not.

As I said - it is a long shot

Otherwise Dittos two suggestions should work. Your water heater circuit - is it on the return pump or a close loop in the sump?

Let me know if it works :)

Sincerely Lasse
 
Last edited:

Lasse

10K Club member
View Badges
Joined
Mar 20, 2016
Messages
10,830
Reaction score
29,794
Location
Källarliden 14 D Bohus, Sweden
Rating - 0%
0   0   0
PS

If it work - you have to set the maximum on time to 0:00:00 (it means No max time) And maybe check the reset auto... box too

Screen Shot 02-02-19 at 11.09 AM.PNG

Sincerely Lasse
 

Ditto

Valuable Member
View Badges
Joined
Apr 25, 2017
Messages
2,229
Reaction score
2,970
Location
Albany, NY
Rating - 0%
0   0   0
Thanks you guys!!!

Totally overlooked the use of the float switches, which I have been using to turn off my sump when the water gets high!!
 
OP
OP
AquaLifeStudio

AquaLifeStudio

Well-Known Member
View Badges
Joined
Mar 7, 2018
Messages
583
Reaction score
580
Location
Fairfield, CA.
Rating - 0%
0   0   0
For the purpose to test this theory I've set the Flow Sensor alarm threshold to be anything less than 2200l/hour as the flow never gets higher than that figure under it's current setup.

"Operation mode" is setup to "Auto top off".

I've configured the "virtual level sensor" to use the signal from the flow sensor which is @ sensor 1. The "state" changes to "fill" but acts intermittently, it wont trigger "alarm". The intermittent action may be due to the slight changes in flow across the sensor as it reads pulses; example: measurement is sent from sensor when the flow changes from 2085l/hour to 2015l/hour.

The Profilix alarm DOES sound and I receive the alarm notification but it is not reflected as an alarm for the "virtual level sensor" that we attempted to setup. In other words, the "state" never displays "alarm".

I did setup the Programmable Logic as detailed above but I dont believe it will work without the alarm properly triggering for the "virtual level sensor".

Any other ideas?
 

Ditto

Valuable Member
View Badges
Joined
Apr 25, 2017
Messages
2,229
Reaction score
2,970
Location
Albany, NY
Rating - 0%
0   0   0
But if we use the basic Alarm Function would it work, it does :)

I just set one of my flows to replicate the same sensor.

I set them very high to replicate the issue easily :)
flow_issue.png


Duplicating the Sensor to another one allows me to set a different value for that one and that the one I want to use to alarm. This allows you to pretty much now set what ever you wish to be the alarm point.

Then I did a Gate Logic (make sure you invert the alarm)
gate_logic.png


Then I assigned the gate Logic to an outlet to test
switch_logic.png


As you can see in this shot the Outlet is on, because I disabled flow sensor 4, but if I enable it because it simulating the flow is low the alarm sounds :)
alarm_whoohoo.png


And S46 is now off
46 is now off.png

This is not a perfect solution, as you could get an alarm for something else, that would shut it off, but using the alarm does work, when the flow drops down below X.

By any chance you have a Float switch inside your Sump we could trigger off that?
 
OP
OP
AquaLifeStudio

AquaLifeStudio

Well-Known Member
View Badges
Joined
Mar 7, 2018
Messages
583
Reaction score
580
Location
Fairfield, CA.
Rating - 0%
0   0   0
Can we use the "fill" as a "state" to work with rather than alarm?

I'm currently playing with the "reaction time" for sensor 1 to see if that can eliminate the intermittent trigger for "fill". It was first set to one second.
 

Ditto

Valuable Member
View Badges
Joined
Apr 25, 2017
Messages
2,229
Reaction score
2,970
Location
Albany, NY
Rating - 0%
0   0   0
I just tried @Lasse ides also and had to set mine to minimum of 5 and got it to work, Return Pump did not work, but Leak Detector did work also, was about 7 seconds after I turned off my return pump.
 
Last edited:

Support@GHLUSA

Team GHL
View Badges
Joined
Jul 27, 2016
Messages
614
Reaction score
418
Rating - 0%
0   0   0
What size heater are you using. S5 is probably not a good socket to use for a heater, it has a lower amp rating due to being a switchable/dimmable socket.
 
OP
OP
AquaLifeStudio

AquaLifeStudio

Well-Known Member
View Badges
Joined
Mar 7, 2018
Messages
583
Reaction score
580
Location
Fairfield, CA.
Rating - 0%
0   0   0
Your water heater circuit - is it on the return pump or a close loop in the sump​

The heater is on the return pump line after a manifold that feeds a few reactors.

20190117_095811.jpg


A Uniseal and some electrical tape wrapped around the very top glass of the heater keep this Eheim Jager from leaking.

I finally replaced the whole section of PVC due to a small leak that came back @ one of the cemented joints. Instead of being 1 1/4" pvc pipe for the heater to sit within, it's now 1 1/2".

20190117_130959.jpg
 

Lasse

10K Club member
View Badges
Joined
Mar 20, 2016
Messages
10,830
Reaction score
29,794
Location
Källarliden 14 D Bohus, Sweden
Rating - 0%
0   0   0
I had a similar problem in one of my jobs. I let the outlet from the filter going down in a bucket above the water level of the sump. The bucket had one "surface holding" hole rather high up in the bucket. The genereal idea was that the water should run into the bucket from above - waterlevel rise and the hole became an outlet. In the bottom there was a tiny hole. A float switch was placed just below the "normal" level. When the flow trough the filter was zero - the tiny hole in the bottom empty the bucket and the float switch change status and the pump stop.

Sincerely Lasse
 