Temperature alarm not triggered?

coweyes298

Active Member
View Badges
Joined
Jun 5, 2017
Messages
459
Reaction score
247
Location
Los Angeles, Diamond Bar, CA
What state or country do you live in
California
Rating - 0%
0   0   0
This is my P4 temperature setting. I think my heater is under power (200 w Jager), with total water volume of 125 ish gallon. These days are cold in SoCal and my temp is dropping to 72.5 this morning... I set the temp sensor to reflect an alarm when the difference is 3.6F but I didn't see any email or text. I am sure my email notification is setting correctly. Below is my setting for temp sensor and also the email notification. Do I did anything wrong in here? By the way I put another 100W Jager into the sump and the temp is slowly climbing back. I am also waiting my new 500W titanium heater to be delivered.
s
upload_2017-12-22_10-18-56.png


upload_2017-12-22_10-23-56.png
 
No alarm was activated because your temperature did not yet go outside of the maximum deviation of 3.6 degrees.

  • Your nominal value (76.46) and Max deviation (3.6) = Alarm will activate when temperature is 72.86F or below. Alarm will also activate when temperature is 80.06F and higher.
 
The screenshot is the current temp value and I understand there is no alarm present. But this morning when I saw the temp is 72.5F I still get no alarm... Wondering what's going wrong.
 
Self test again. I check the email notification and test it and I can receive the notification on both my cell phone text and email.

I then change the temp setting as follow:
upload_2017-12-22_11-3-31.png


I should get alarm when the temp is lower than 77 - 3.6 = 73.4 F.

But I didn't receive any... The P4 front display didn't show up alarm either. Something is wrong...
 
Updated. While messing the max deviation on the temp sensor I found something interesting. I typed 1 F in the max deviation on the temp alarm section the system automatically changed 1 F I input to 1.8 F. If I put 2 F it changed to 3.6 F and so on. It looks like system auto multiply 1.8 F for what your input is. And if I put 1 F (it will change to 1.8 F after the 1 F input), I get the alarm. But when I input 2 F (actually 3.6 F) no alarm triggered...

@Vinny@GHLUSA @Marco@GHLUSA do you know what is going on for this?
 