Using ground probes in aquariums

OP
OP
Brew12

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,020
Location
Decatur, AL
Rating - 0%
0   0   0
upload_2016-10-25_13-18-30.png
Excellent information! It shows that a properly functioning 20 Amp breaker will trip under 25 amps even if it is at -10C.

The older UL tests were done at 25C but otherwise it hasn't changed much.
 

Scubado63

Community Member
View Badges
Joined
Jan 12, 2015
Messages
91
Reaction score
25
Location
Clermont , Florida
Rating - 0%
0   0   0
Brew12, How did you connect your GFCI outlets to the Apex outlets, I assume it is the 4 empty outlet on the apex, but how did you wire them
 
OP
OP
Brew12

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,020
Location
Decatur, AL
Rating - 0%
0   0   0
Brew12, How did you connect your GFCI outlets to the Apex outlets, I assume it is the 4 empty outlet on the apex, but how did you wire them
It is the 4 outlets with the plugs. The picture was taken early in my build. I cut the cords off of a few power strips, prepped the cut ends and wired them into the GFCI's. After that, I just plugged the cord into the outlet on the Apex. Very simple.
 

Paul B

10K Club member
View Badges
Joined
Nov 3, 2010
Messages
17,950
Reaction score
60,785
Location
Long Island NY
Rating - 0%
0   0   0
What about metal in the water? Since the grounding probe is made of metal, surely that much leach into the water which cant be good for sps corals and sensitive invertebrates. Even if its stainless steel it will leach chrome, nickel and molybden or is it made out of titantium or any other reef safe metal?

So I guess this would be bad! :rolleyes:

 

jasonrusso

2500 Club Member
View Badges
Joined
Apr 21, 2014
Messages
3,252
Reaction score
2,389
Location
Haverhill, MA
Rating - 0%
0   0   0
What about metal in the water? Since the grounding probe is made of metal, surely that much leach into the water which cant be good for sps corals and sensitive invertebrates. Even if its stainless steel it will leach chrome, nickel and molybden or is it made out of titantium or any other reef safe metal?
This is the one I bought. It's titanium.


Deep Blue Professional ADB12000 Ground Control Ti Probe for Aquarium https://www.amazon.com/dp/B005DGKCF4/ref=cm_sw_r_cp_apa_Yg.dybQ5PMNP8
 

jasonrusso

2500 Club Member
View Badges
Joined
Apr 21, 2014
Messages
3,252
Reaction score
2,389
Location
Haverhill, MA
Rating - 0%
0   0   0
I think it is just another option. You can bolt it to the outlet box, etc. You don't have to use both.

Yes, only the ground is metal.
 

RobBaglieri

Active Member
View Badges
Joined
Aug 1, 2016
Messages
178
Reaction score
97
Location
Douglas MA
Rating - 0%
0   0   0
Yes, you should still find out what is leaking. You probably have a piece of electrical equipment that is failing. It could be leaching metals like copper or other materials into your tank water. I would make it a priority to find it and remove it.
A great way to troubleshoot it is to buy a temporary GFCI plug like the one I am linking. Plug your components in one at a time until (with your ground probe installed) and see which one trips the GFCI.

http://www.homedepot.com/p/YELLOW-JACKET-GFCI-Portable-Plug-In-Adapter-Black-2762/204667709
this is the plug I temporarily have on my tank. I originally bought it to use with powertools outdoors when a GFCI outlet was not available. It works great. One drawback with this particular item, if there is a power outage, it must be manually reset once the power comes back on.
 

spllbnd2

Active Member
View Badges
Joined
Dec 1, 2014
Messages
178
Reaction score
117
Location
Edmonds, Washington
Rating - 0%
0   0   0
Where does that round thing go? Is that outlet made of plastic except for the grounding part?


The round terminal would be used ONLY if you are using it with a metal box. When you use that in a plastic box it does nothing.

Think of it like this, metal screw that holds the outlet plate onto the box goes into... Plastic, no path to ground. While on a metal box that same screw that holds the outlet cover in place goes to? You guessed it, metal and onward to the ground screw that should be installed in the box per NEC.

This is know as a bonding jumper wire.

250.146 (A) Surface Mounted Box. Where the box is mounted on the surface, direct metal to metal contact between the device yoke and the box or a contact yoke or a self grounding receptacle shall be permitted to ground the receptacle to the box.

250.146 (B) Contact Devices or Yokes. Contact devices or yokes designed and listed as self-grounding shall be permitted in conjunction with the supporting screws to establish the grounding circuit between the device yoke and flush type boxes.

outlet.jpg
receptacle.jpg

Cheers,
Alex
 
Last edited:

jasonrusso

2500 Club Member
View Badges
Joined
Apr 21, 2014
Messages
3,252
Reaction score
2,389
Location
Haverhill, MA
Rating - 0%
0   0   0
The round terminal would be used ONLY if you are using it with a metal box. When you use that in a plastic box it does nothing.

Think of it like this, metal screw that holds the outlet plate onto the box goes into... Plastic, no path to ground. While on a metal box that same screw that holds the outlet cover in place goes to? You guessed it, metal and onward to the ground screw that should be installed in the box per NEC.

Cheers,
Alex
Absolutely correct! I was under the assumption that people would realize that plastic boxes aren't grounded, but I guess not everyone is familiar with home wiring.
 

Vidofner

Community Member
View Badges
Joined
Feb 13, 2013
Messages
89
Reaction score
64
Location
Sweden
Rating - 0%
0   0   0
Your outlets look alot different than european outlets. Ive never seen anything similar to what you call bonding jumping wire :)
 
OP
OP
Brew12

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,020
Location
Decatur, AL
Rating - 0%
0   0   0
Your outlets look alot different than european outlets. Ive never seen anything similar to what you call bonding jumping wire :)
I have to give you Europeans credit, you have a much safer distribution and home wiring system than we use in the US.
 

Vidofner

Community Member
View Badges
Joined
Feb 13, 2013
Messages
89
Reaction score
64
Location
Sweden
Rating - 0%
0   0   0
I have to give you Europeans credit, you have a much safer distribution and home wiring system than we use in the US.
However, we need to deal with 220 volts instead of 110 when **** hit the fan. Ive done that. Was a scary feeling. My arm shook for like 10min after it.
 
OP
OP
Brew12

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,020
Location
Decatur, AL
Rating - 0%
0   0   0
However, we need to deal with 220 volts instead of 110 when **** hit the fan. Ive done that. Was a scary feeling. My arm shook for like 10min after it.
Fair point, but we use 220V also. We only use it in more limited applications like for ovens, air conditioning and electric clothes dryers.

On thing that is often overlooked is that 50hz is less likely to cause ventricular fibrillation than 60hz is. I haven't seen a reason for that but Europeans are less likely to suffer heart failure during an electrical shock and have higher survival rates despite the higher voltage.
 

Vidofner

Community Member
View Badges
Joined
Feb 13, 2013
Messages
89
Reaction score
64
Location
Sweden
Rating - 0%
0   0   0
Fair point, but we use 220V also. We only use it in more limited applications like for ovens, air conditioning and electric clothes dryers.

On thing that is often overlooked is that 50hz is less likely to cause ventricular fibrillation than 60hz is. I haven't seen a reason for that but Europeans are less likely to suffer heart failure during an electrical shock and have higher survival rates despite the higher voltage.
Also you got alot higher ampere. I don't have much electrical knowledge but i think I've read that you got 15 A in your outlets and our normal outlets faults out at 10. I think they usually keep at 2.5
 

jasonrusso

2500 Club Member
View Badges
Joined
Apr 21, 2014
Messages
3,252
Reaction score
2,389
Location
Haverhill, MA
Rating - 0%
0   0   0
Also you got alot higher ampere. I don't have much electrical knowledge but i think I've read that you got 15 A in your outlets and our normal outlets faults out at 10. I think they usually keep at 2.5
230v at 10a is 2300 watts. 120v at 15A is 1800 watts. Europe carries more power.
 
OP
OP
Brew12

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,020
Location
Decatur, AL
Rating - 0%
0   0   0
But 10A is when our fuses goes so we don't usually operate with 10A. What I've read it's normally 2,5A
From a safety perspective, your higher system voltage or lower trip point doesn't make much difference. The majority of electrical shocks occur from a live conductor to ground. In Europe, you have 2 legs that are both 110V to ground. In the US, we typically have 1 leg at 115V to ground with the other leg being grounded. Because of this, the voltage we would typically be shocked by are almost identical.
When 0.1 Amps for 2 seconds is considered a fatal exposure, it doesn't much matter if your fuses or breakers trip at 2.5A, 10A or 20A.
 