I'm doing a build in which I will have (2) overflow boxes, each connected to 1" PVC.

I plan on a 1" PVC return which will split once inside the tank.

The problem is that the intended return pump outlet is only threaded 3/4".

Can I do a return that is only 3/4" PVC?

I suppose I can get a connector that goes from 3/4" to 1", but my concern is that the flow OUT will be greater than the flow IN.

The intended return pump has the capability to keep up with the overflow, but I am wondering about the 1/4" diameter difference in the return.

Feedback?
Dom
 

Larry L

Valuable Member
View Badges
Joined
Nov 4, 2014
Messages
1,348
Reaction score
1,389
Location
x
Rating - 0%
0   0   0
Not exactly sure if this is what you're asking, but I think you are thinking about it backwards - it's the overflow that needs to keep up with the return pump, not the other way around. The only water that can overflow back to the sump is the water that the return pump is putting into in the tank - there's no way the overflow will send more water to the sump than the return pump is sending to the tank in the first place. In fact, you usually want your overflow plumbing to be oversized compared to your return, just to make sure that even if there is a small amount of clogging in the overflow, all the water sent to the tank still makes it down the overflow.
 

redfishbluefish

Stay Positive, Stay Productive
View Badges
Joined
Mar 22, 2012
Messages
12,314
Reaction score
25,445
Location
Sayreville, NJ
Rating - 0%
0   0   0
I would immediately step up the return to 1 inch....you'll have less headloss.
 

jgvergo

Valuable Member
View Badges
Joined
Nov 29, 2014
Messages
1,307
Reaction score
1,368
Location
New York
Rating - 0%
0   0   0
I would immediately step up the return to 1 inch....you'll have less headloss.
I'm pretty sure the head loss will increase if the return line increases in diameter. The pump has to push up a larger volume of water.
 

redfishbluefish

Stay Positive, Stay Productive
View Badges
Joined
Mar 22, 2012
Messages
12,314
Reaction score
25,445
Location
Sayreville, NJ
Rating - 0%
0   0   0
I'm pretty sure the head loss will increase if the return line increases in diameter. The pump has to push up a larger volume of water.

It might be counterintuitive, but larger pipe diameter lowers the frictional loss per volume of water, causing for greater flow. Go to any of the headloss calculators, pick any pump and some length of pipe and now look at two different diameters.....the smaller the pipe, the greater the headloss.
 

doughboy

Well-Known Member
View Badges
Joined
Feb 20, 2010
Messages
563
Reaction score
302
Location
Norcal
Rating - 0%
0   0   0
you can look at it this way

1" cross section is roughly double 3/4" cross section area.
so if you push less water using 3/4", but you need to push twice as much compared to 1", so in effect, the 3/4" has to travel twice the distance of 1" to get the same volume, thus have to overcome twice the friction.
 
OP
OP
Dom

Dom

Theoretical Reef Keeper
View Badges
Joined
Apr 29, 2016
Messages
7,783
Reaction score
8,226
Location
NY
Rating - 0%
0   0   0
Not exactly sure if this is what you're asking, but I think you are thinking about it backwards - it's the overflow that needs to keep up with the return pump, not the other way around. The only water that can overflow back to the sump is the water that the return pump is putting into in the tank - there's no way the overflow will send more water to the sump than the return pump is sending to the tank in the first place. In fact, you usually want your overflow plumbing to be oversized compared to your return, just to make sure that even if there is a small amount of clogging in the overflow, all the water sent to the tank still makes it down the overflow.

That makes perfect sense to me; you can only remove at the rate at which water is returned to the display.
 

jgvergo

Valuable Member
View Badges
Joined
Nov 29, 2014
Messages
1,307
Reaction score
1,368
Location
New York
Rating - 0%
0   0   0
It might be counterintuitive, but larger pipe diameter lowers the frictional loss per volume of water, causing for greater flow. Go to any of the headloss calculators, pick any pump and some length of pipe and now look at two different diameters.....the smaller the pipe, the greater the headloss.
Sure enough... Live and learn!
 