Shocked by Grounding Probe

michaelh83

New Member
View Badges
Joined
Jun 24, 2025
Messages
1
Reaction score
0
Location
Orlando, FL
What state or country do you live in
Florida
Rating - 0%
0   0   0
I’m experiencing an issue when I connect the grounding probe to the outlet and touch the water barfoot. Surprisingly, the water shocks me, and there’s no GFCI trip or anything.

However, when I unplug the grounding probe and touch the water, I don’t feel anything.

I’m curious to know why I only get shocked when the grounding probe is connected?

To investigate further, I used a voltmeter to measure the voltage, and it jumps around 4 volts, reaching up to 6 volts when the ATO is measuring water with the grounding probe not connected to the aquarium.

I’ve also tested the outlet Nutral to Ground, and it reads 0 volts.


Breakers are Arc Fault
Outlet is GFCI

Equipment
  • Red Sea ATO
  • Reef LED 115 G2
  • ReefMat 250
  • ReefRun 4000 G2
  • ReefWave 25
  • Reefer DC Skimmer 300
  • Helio 200 Watt PTC Smart Heater
 
For those in Dark Mode:

"I’m experiencing an issue when I connect the grounding probe to the outlet and touch the water barfoot. Surprisingly, the water shocks me, and there’s no GFCI trip or anything.

However, when I unplug the grounding probe and touch the water, I don’t feel anything.

I’m curious to know why I only get shocked when the grounding probe is connected?

To investigate further, I used a voltmeter to measure the voltage, and it jumps around 4 volts, reaching up to 6 volts when the ATO is measuring water with the grounding probe not connected to the aquarium.

I’ve also tested the outlet Nutral to Ground, and it reads 0 volts. "
 
What are you standing on? Dry floor? Concrete? Carpet?

How is the outlet grounded? Good copper all the way from the green screw on the outlet to the breaker box? Is the breaker box ground bar connected to earth thru you copper main water supply it another means?

There must be a voltage differential between what you are standing on and the ground in your outlet. It should be measurable.
 
For those in Dark Mode:

"I’m experiencing an issue when I connect the grounding probe to the outlet and touch the water barfoot. Surprisingly, the water shocks me, and there’s no GFCI trip or anything.

However, when I unplug the grounding probe and touch the water, I don’t feel anything.

I’m curious to know why I only get shocked when the grounding probe is connected?

To investigate further, I used a voltmeter to measure the voltage, and it jumps around 4 volts, reaching up to 6 volts when the ATO is measuring water with the grounding probe not connected to the aquarium.

I’ve also tested the outlet Nutral to Ground, and it reads 0 volts. "
You have a high resistance or faulty ground
 

TOP 10 Trending Threads

WHAT FIRST SPARKED YOUR INTEREST IN REEFING?

  • I saw a reef tank that hooked me

    Votes: 11 28.9%
  • I was already keeping freshwater aquariums

    Votes: 13 34.2%
  • A particular fish got me interested

    Votes: 7 18.4%
  • Corals and inverts were the draw

    Votes: 6 15.8%
  • A friend or family member introduced me

    Votes: 5 13.2%
  • The science and ecosystem challenge appealed to me

    Votes: 6 15.8%
  • I stumbled into it… and here we are

    Votes: 3 7.9%
  • Other (Post in the comments)

    Votes: 6 15.8%
Back
Top
Home
Post thread…
Market
What's new