I’m experiencing an issue when I connect the grounding probe to the outlet and touch the water barfoot. Surprisingly, the water shocks me, and there’s no GFCI trip or anything.

However, when I unplug the grounding probe and touch the water, I don’t feel anything.

I’m curious to know why I only get shocked when the grounding probe is connected?

To investigate further, I used a voltmeter to measure the voltage, and it jumps around 4 volts, reaching up to 6 volts when the ATO is measuring water with the grounding probe not connected to the aquarium.

I’ve also tested the outlet Nutral to Ground, and it reads 0 volts.


Breakers are Arc Fault
Outlet is GFCI

Equipment
  • Red Sea ATO
  • Reef LED 115 G2
  • ReefMat 250
  • ReefRun 4000 G2
  • ReefWave 25
  • Reefer DC Skimmer 300
  • Helio 200 Watt PTC Smart Heater
 

MoeStachio

Active Member
View Badges
Joined
May 22, 2025
Messages
312
Reaction score
429
Location
Edmonton
Rating - 0%
0   0   0
For those in Dark Mode:

"I’m experiencing an issue when I connect the grounding probe to the outlet and touch the water barfoot. Surprisingly, the water shocks me, and there’s no GFCI trip or anything.

However, when I unplug the grounding probe and touch the water, I don’t feel anything.

I’m curious to know why I only get shocked when the grounding probe is connected?

To investigate further, I used a voltmeter to measure the voltage, and it jumps around 4 volts, reaching up to 6 volts when the ATO is measuring water with the grounding probe not connected to the aquarium.

I’ve also tested the outlet Nutral to Ground, and it reads 0 volts. "
 

Submerge

Active Member
View Badges
Joined
Jul 23, 2025
Messages
210
Reaction score
334
Location
St. Louis
Rating - 0%
0   0   0
What are you standing on? Dry floor? Concrete? Carpet?

How is the outlet grounded? Good copper all the way from the green screw on the outlet to the breaker box? Is the breaker box ground bar connected to earth thru you copper main water supply it another means?

There must be a voltage differential between what you are standing on and the ground in your outlet. It should be measurable.
 

gbroadbridge

5000 Club Member
View Badges
Joined
Mar 25, 2021
Messages
5,405
Reaction score
5,607
Location
Sydney, Australia
Rating - 0%
0   0   0
For those in Dark Mode:

"I’m experiencing an issue when I connect the grounding probe to the outlet and touch the water barfoot. Surprisingly, the water shocks me, and there’s no GFCI trip or anything.

However, when I unplug the grounding probe and touch the water, I don’t feel anything.

I’m curious to know why I only get shocked when the grounding probe is connected?

To investigate further, I used a voltmeter to measure the voltage, and it jumps around 4 volts, reaching up to 6 volts when the ATO is measuring water with the grounding probe not connected to the aquarium.

I’ve also tested the outlet Nutral to Ground, and it reads 0 volts. "
You have a high resistance or faulty ground
 

TOP 10 Trending Threads

WHAT AMOUNT OF LIVE ROCK AND SAND SHOULD BE PRIORITIZED FOR OPTIMAL BIODIVERSITY/FILTRATION?

  • 100% live rock + bagged sand

    Votes: 34 28.1%
  • 100% dry rock + 100% live sand

    Votes: 41 33.9%
  • 50/50 live/dry rock, 50/50 live/bagged sand

    Votes: 27 22.3%
  • 75% live rock, 25% live sand

    Votes: 11 9.1%
  • 25% live rock, 75% live sand

    Votes: 8 6.6%
Back
Top