Gas DryerLooks like he’s running a gas dryer.
I happen to have my 2020 NEC in front of me.... It's based on not overloading the circuit since the water heaters in some washing machines can pull more than 15A so having another load could easily exceed the 80% limit. Built in microwaves have a similar requirement.
2010.11 (C) 2 Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20A branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
I am very ill versed in residential code but I believe at least one ded per code in laundry room.Does that apply to all circuits in the laundry room?
I am very ill versed in residential code but I believe at least one ded per code in laundry room.
They definitely went above and beyond. They did that as well in my house.From his pictures it looks like he has two one for the washer and one for the dryer. I did not know if he could switch out the one that the dryer is plugged into since it is a 20 amp also. I have not had to do much code research at work in awhile so I am not current either.
No, it only applies the the receptacle for the washing machineDoes that apply to all circuits in the laundry room?
From the looks of it, that splitter is rated at no more than 15A. Did you verify your washing machine uses less than 15A?Junk drawer never fails!
So should I just leave the adaptor plugged on as I showed in the pic?I happen to have my 2020 NEC in front of me.... It's based on not overloading the circuit since the water heaters in some washing machines can pull more than 15A so having another load could easily exceed the 80% limit. Built in microwaves have a similar requirement.
2010.11 (C) 2 Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20A branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
No, it only applies the the receptacle for the washing machine
From the looks of it, that splitter is rated at no more than 15A. Did you verify your washing machine uses less than 15A?
I didn't notice that there were 2 separate 120V outlets, completely missed that. Yes, it would be fine to switch the one for the dryer. A 120V dedicated dryer circuit should never be required. If a dryer is electric, it will need the 220V outlet. If it is gas, the electric is categorized as a small appliance which do not require dedicated outlets.So switching the one that the dryer is plugged in would be good to switch to a duplex.
Since your washer only pulls a max of 10A it should be fine as is, as long as that splitter is rated for 15A. If you don't know the splitter rating, I'd replace it with a new one, they are cheap. Just keep in mind if you replace your washing machine you may need to change how you connect this. The easiest change would be to switch it from your washing machine to where your dryer plugs in.So should I just leave the adaptor plugged on as I showed in the pic?
I have two 20’s one behind the washer and one behind the dryerFrom his pictures it looks like he has two one for the washer and one for the dryer. I did not know if he could switch out the one that the dryer is plugged into since it is a 20 amp also. I have not had to do much code research at work in awhile so I am not current either.
That is what i thought from the pictures.I have two 20’s one behind the washer and one behind the dryer
In addition to the 220 and the gas connection
I personally would NOT use this or any other adapter. They generally are not meant for permanent installation and they can be fire hazards when used permanently with higher amp draws. (Despite rating) Some threads on here and reef central showing these things melted. Might as well do it right.Junk drawer never fails!
That seems like a lot of work to power a 1/2 amp booster pump.ultimately, if it was me needing this in my house, I’d convert the dryer outlet to (2) ded 20a outlets and replace the breaker to a 2-pole 20a gfci breaker. The wiring within the jbox should consist of 2 hots (blk,red) a neutral and a ground. Share the neutrals and grounds and one hot to one plug the other plug gets remaining hot. If you ever sell the house just revert to original.
Awesome! Sounds like a super easy fix and no alterations and I just confirmed the plug is 15A.I didn't notice that there were 2 separate 120V outlets, completely missed that. Yes, it would be fine to switch the one for the dryer. A 120V dedicated dryer circuit should never be required. If a dryer is electric, it will need the 220V outlet. If it is gas, the electric is categorized as a small appliance which do not require dedicated outlets.
Since your washer only pulls a max of 10A it should be fine as is, as long as that splitter is rated for 15A. If you don't know the splitter rating, I'd replace it with a new one, they are cheap. Just keep in mind if you replace your washing machine you may need to change how you connect this. The easiest change would be to switch it from your washing machine to where your dryer plugs in.
I’ve changed receptacles before. I just don’t want to be in violation of anything.I’d replace the outlet for the Washer with a 20 Amp. GFCI Receptacle. Unless the Breaker for the Washer is a GFCI. If so use a 20 Amp. Duplex Receptacle. Note; that there is a difference between a 15 Amp. and a 20 Amp. Receptacle. Pull the Washer Plug, Plug a known working light into the Receptacle, turn the breaker off before changing out, and check to see if the light doesn’t work. I would watch several YouTube Videos on how to change a Receptacle out.
You can't plug a 20 amp plug into a 15 amp receptacle or adapter. It won't fit.From the looks of it, that splitter is rated at no more than 15A. Did you verify your washing machine uses less than 15A?
I do, one at each entrance so either can turn light on or offDo you have a wall switch for lighting? Those typically have 120v inside.