So I am installing a lot of wire in my house because it was all done with 12/2 without ground probably back sometime in the 50's. Some of the house has more up to date electrical. In the process I found out my grounding terminal in my 100A sub-panel is full. Is there any way to extend this terminal? It only had 6 or so ports.
 

DaveMorris

MACNA2016 Co-Chair
View Badges
Joined
May 9, 2009
Messages
786
Reaction score
495
Location
San Diego, CA
Rating - 0%
0   0   0
You can add an additional ground bar in the box if you have room for it. Grounding usually is connected to the box itself so it should be very easy. That being said, if you have any doubts, I would get an electrician to do it. Local codes and things unique to your particular scenario could be different.
 

ReeferBob

Valuable Member
View Badges
Joined
Jan 20, 2013
Messages
1,505
Reaction score
588
Location
Damascus, MD
Rating - 0%
0   0   0
Usually you can put two wires in each hole of the gounding bar. Also I suspect your house does have a ground. You may not have 3 prong outlets, but the ground is there connected to the metal box so the 2 prong plugs are grounded since they touch the box. You can just replace them with a 3 prong outlet and it will also be grounded since it also touches the metal box.
 
OP
OP
Chameleon

Chameleon

Valuable Member
View Badges
Joined
Jan 5, 2012
Messages
2,249
Reaction score
93
Location
Rockville, MD
Rating - 0%
0   0   0
Usually you can put two wires in each hole of the gounding bar. Also I suspect your house does have a ground. You may not have 3 prong outlets, but the ground is there connected to the metal box so the 2 prong plugs are grounded since they touch the box. You can just replace them with a 3 prong outlet and it will also be grounded since it also touches the metal box.
is it safe to put two in one? I would think they are designed to hold one and putting two may result in a clamp failure later. All outlets are 3 prong, but the wire is all 12/2 no G. I have spent some time reworking the electrical on two circuits already(was 1 15A circuit but it was like half the house including kitchen, office, bathroom, attic, and outdoor lights, yikes!) and while its all roughed in I haven't gotten it into the box yet. There was some 14 gauge wire used here and there, but now everything is either 12/2G or 12/3G (3 way switches). I divided it into two circuits and one will be 20A and the other I will be keeping the 15A breaker for now. Now I am at the point where I am about ready to cut a hole in the wall to access the outside of my recessed sub-panel, but realized I didn't have enough ground terminals so I am holding off until I get the issue resolved.
 
OP
OP
Chameleon

Chameleon

Valuable Member
View Badges
Joined
Jan 5, 2012
Messages
2,249
Reaction score
93
Location
Rockville, MD
Rating - 0%
0   0   0
You can add an additional ground bar in the box if you have room for it. Grounding usually is connected to the box itself so it should be very easy. That being said, if you have any doubts, I would get an electrician to do it. Local codes and things unique to your particular scenario could be different.
I saw the extended grounding bards at the hardware store. This will probably be the route I choose I just need to make sure I am doing it the right way. I didn't want to extend a ground that shouldn't be extended. Time for some research on my part. Thanks for the help!
 
OP
OP
Chameleon

Chameleon

Valuable Member
View Badges
Joined
Jan 5, 2012
Messages
2,249
Reaction score
93
Location
Rockville, MD
Rating - 0%
0   0   0
Just and idea of what I am working with....the old electrical had splices not in boxes with about 18'' of exposed wire(insulated) with tension stress on the splice sites and yellow nuts for 4 wire splices...fun fun
 

ReeferBob

Valuable Member
View Badges
Joined
Jan 20, 2013
Messages
1,505
Reaction score
588
Location
Damascus, MD
Rating - 0%
0   0   0
Yes it is perfectly safe and I am pretty sure code to share the ground bar with more then one ground in each hole. My box has 2 in each hole and that is how the electrician wired it.

Also don't forget NO hidden junction boxes! Even if that means you need to rewire all of those splices.
 
OP
OP
Chameleon

Chameleon

Valuable Member
View Badges
Joined
Jan 5, 2012
Messages
2,249
Reaction score
93
Location
Rockville, MD
Rating - 0%
0   0   0
Yes it is perfectly safe and I am pretty sure code to share the ground bar with more then one ground in each hole. My box has 2 in each hole and that is how the electrician wired it.

Also don't forget NO hidden junction boxes! Even if that means you need to rewire all of those splices.

Thanks! I am in the process of rewiring everything. By hidden what exactly do they mean? Does that mean not behind drywall? I am doing most of the stuff in the attic so I dont think it should be a problem. Do they mean you cant cover it with insulation? Ill look into it.
 

redfishbluefish

Stay Positive, Stay Productive
View Badges
Joined
Mar 22, 2012
Messages
12,312
Reaction score
25,436
Location
Sayreville, NJ
Rating - 0%
0   0   0
You say the wiring is 12/2 with no ground. However, if it is BX wire (metal sheathed wire), that outer metal sheath is the ground.
 

redfishbluefish

Stay Positive, Stay Productive
View Badges
Joined
Mar 22, 2012
Messages
12,312
Reaction score
25,436
Location
Sayreville, NJ
Rating - 0%
0   0   0
its not...that is just old cloth wrapped wire....

Ouch! You have OLD two wire Romex wire. Although the national code allows individual ground wires to be run toexisting “grounded” circuits, some local codes do not allow this. You’re best bet is to do what you aredoing, replace with new “grounded” romex or BX, if your local code requires BX.
 

Reef Pets

Bioprospector
View Badges
Joined
Mar 7, 2008
Messages
10,025
Reaction score
1,428
Location
Ohio
Rating - 0%
0   0   0
Yes, it is safe and not against code to put more than one ground wire per terminal. You should be able to fit three 12 gauge wires in one hole. I'm a a licensed electrician therefore I can assure you that the information is correct. I've wired more houses than I care to remember...
 

Bow

Well-Known Member
View Badges
Joined
Apr 3, 2013
Messages
616
Reaction score
2
Location
Long island
Rating - 0%
0   0   0
If its a sub panel the grounds and neutrals should be separated. If you only have one panel in the house then you can put 2 wires under the same lug, try to use the same size wire.
 

ReeferBob

Valuable Member
View Badges
Joined
Jan 20, 2013
Messages
1,505
Reaction score
588
Location
Damascus, MD
Rating - 0%
0   0   0
Thanks! I am in the process of rewiring everything. By hidden what exactly do they mean? Does that mean not behind drywall? I am doing most of the stuff in the attic so I dont think it should be a problem. Do they mean you cant cover it with insulation? Ill look into it.

You can have a junction box in an attic. You can't have one hidden behind drywall. I think the blown in insulation would be ok to cover it but not the R-22 stuff.
 

OrionN

Anemones
View Badges
Joined
Jul 28, 2013
Messages
11,302
Reaction score
22,513
Location
Corpus Christi, TX
Rating - 0%
0   0   0
Just from that one picture you posted, I am sure that your electrical is not up to code. Did you have an inspection before you buy your house? You may want too get an electrician to insect your house, then you know what you are dealing with.
 

Coral Hind

New Member
View Badges
Joined
Mar 30, 2010
Messages
2
Reaction score
0
Location
VA
Rating - 0%
0   0   0
Yes, it is safe and not against code to put more than one ground wire per terminal. You should be able to fit three 12 gauge wires in one hole. I'm a a licensed electrician therefore I can assure you that the information is correct. I've wired more houses than I care to remember...

It may be fine according to the NEC but that is just a general guideline and the local code enforcement office might not allow it. It's best to always check with your local inspector since what might work in one guys state might not work in another.

Also, was the panel approved to allow double tapping on a ground screw? If your house burned down and the insurance company or fire inspector found out you didn't wired the panel to how it was designed or intended you would be in a tight spot getting the claim paid. Just something to think about.
 

ReeferBob

Valuable Member
View Badges
Joined
Jan 20, 2013
Messages
1,505
Reaction score
588
Location
Damascus, MD
Rating - 0%
0   0   0
It may be fine according to the NEC but that is just a general guideline and the local code enforcement office might not allow it. It's best to always check with your local inspector since what might work in one guys state might not work in another.

Also, was the panel approved to allow double tapping on a ground screw? If your house burned down and the insurance company or fire inspector found out you didn't wired the panel to how it was designed or intended you would be in a tight spot getting the claim paid. Just something to think about.

The only thing I agree with here is that the box should be rated for multiple wires in each ground terminal. The insurance part is totally wrong but a common misconception. Doesn't NEC = NATIONAL electrical code?
 

OrionN

Anemones
View Badges
Joined
Jul 28, 2013
Messages
11,302
Reaction score
22,513
Location
Corpus Christi, TX
Rating - 0%
0   0   0
Just from that picture of the spice wire not in a junction box, that house electical is not up to code. If you have to ask for help online, you need to get a profesional to look at the whole house.
 
OP
OP
Chameleon

Chameleon

Valuable Member
View Badges
Joined
Jan 5, 2012
Messages
2,249
Reaction score
93
Location
Rockville, MD
Rating - 0%
0   0   0
I did have an inspection, and the old un-grounded electrical was identified and we worked that into the contract price.

Also an electrician (family friend) did come by and give me some pointers and tips for the rewire. We put in a 20A circuit off the main 200A panel to the basement for the fish tank so I could get my feet wet and see how the work is done. The issue about the sub-panel being limited on grounding terminals did not come up at the time.
 
OP
OP
Chameleon

Chameleon

Valuable Member
View Badges
Joined
Jan 5, 2012
Messages
2,249
Reaction score
93
Location
Rockville, MD
Rating - 0%
0   0   0
And thanks for the tips everyone....sounds like I will have an easy fix of just using terminals for multiple wires, but I'll check the local codes to be sure
 

TOP 10 Trending Threads

HOW DO YOU ADJUST YOUR CUC AS ALGAE DISAPPEARS?

  • Capture and re-home CUC

    Votes: 8 7.3%
  • Increase white light/hours in tank to spur algae growth to feed CUC

    Votes: 6 5.5%
  • Feed nori to support CUC

    Votes: 39 35.5%
  • Feed herbivore pellets to support CUC

    Votes: 39 35.5%
  • Allow attrition to balance CUC and algae

    Votes: 46 41.8%
  • Provide macro algae to feed CUC

    Votes: 7 6.4%
  • Introduce CUC predators

    Votes: 1 0.9%
  • Other (please explain)

    Votes: 11 10.0%
Back
Top