Since you ran 12/3, use one as the hot, one as the neutral, and one as the ground. Keep the circuits completely separate imo.@Brew12, thanks for the quick feed back, your right, I'm keeping it 2 separate 120V lines, just wanted to use my resources here on Reef2reef to do it right.
If you're sharing the neutral in one of these so called multi-wire circuits you have to tie the breakers together because the potential from one circuit would make the other one hot even if it's discreet breaker was tripped or shutoff.
I agree that it's a bad idea. I'm not sure why people think they are good or even useful. They will work at least if you have purely resistive loads like incandescent light bulbs. I'm not sure how having unbalanced inductive loads like return pumps and powerheads would behave though. I also seem to remember lighting ballasts do not do well at all in these type of arrangements.
I would say that both are bad. You don't want shared neutral or tied breakers on 120v system imo.ok now I'm confused, kind of getting a 50/50 on this project. using a 12/3 wire, which has a red, black, white and bare wire, @fermentedhiker are you saying using the two hots and shared neutral is bad? or having the breakers tied is bad?
ok now I'm confused, kind of getting a 50/50 on this project. using a 12/3 wire, which has a red, black, white and bare wire, @fermentedhiker are you saying using the two hots and shared neutral is bad? or having the breakers tied is bad?
the interesting thing about thinking of this12/3 two line set up, I got the idea from a quote of a major electrical company that was going to install it for me that way for an extra 150 dollars.….
You see shared neutrals on 277V lighting systems fairly regularly. It is a horrible practice. It works fine as long as the current of both hots together is within the rating of the neutral. You don't typically see it in non lighting circuits because it is easy to overload the neutral wire. It also makes troubleshooting ground faults a pain.They were going to charge you extra to do something that used less material? I think these types of circuits had a specific purpose in situations where the loads were almost identical, but I can't see using them on two circuits with essentially random loads would make sense. To be clear I've not run across a single instance of a licensed electrician installing one in a residential application. Commercial stuff is outside of my wheelhouse though.
You see shared neutrals on 277V lighting systems fairly regularly. It is a horrible practice. It works fine as long as the current of both hots together is within the rating of the neutral. You don't typically see it in non lighting circuits because it is easy to overload the neutral wire. It also makes troubleshooting ground faults a pain.
But, functionally, it works. All of your neutrals are tied together and to ground in your electrical panel so from a theory perspective, it shouldn't cause any issues doing it that way. That doesn't make it a good idea.
They were going to charge you extra to do something that used less material?
You see shared neutrals on 277V lighting systems fairly regularly. It is a horrible practice. It works fine as long as the current of both hots together is within the rating of the neutral. You don't typically see it in non lighting circuits because it is easy to overload the neutral wire. It also makes troubleshooting ground faults a pain.
But, functionally, it works. All of your neutrals are tied together and to ground in your electrical panel so from a theory perspective, it shouldn't cause any issues doing it that way. That doesn't make it a good idea.
A shared neutral, if done correctly, will still work with GFCI circuits.the extra price was going from 12/2 to 12/3
looking at how the neutrals are all tied together with the grounds was why I thought the shared neutral will be ok in the first place, but the current coming back on the one neutral not being even could be an issue also during a google search I saw a warning about sharing a neutral on a gfci outlet would not work because it would cause a trip detecting the different current
Can i join neutral like this ? It's going to an 8 channel relay that's connected to a Feef-PiAfter 25 years experiance on the field and 15 years at the office, as an electrican I think I can answer most of your questions.
Thanks to my fellow electricians for helping answering your question's.
And the team is:
Myself and
anemonekeeper
:wink:
Can i join neutral like this ? It's going to an 8 channel relay that's connected to a Feef-Pi
thank you you rock!Yes ..
Usually newer GFCI receptacles have the light on when it's working. So are you saying that you cannot reset the GFCI?It has a gfci outlet set up but when I press reset a light pops up red and nothing else happens.